We’d like to remind Forumites to please avoid political debate on the Forum.

This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.

📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
The Forum now has a brand new text editor, adding a bunch of handy features to use when creating posts. Read more in our how-to guide

Freezing Cold boiler wont stay lit

2»

Comments

  • rustyboy21
    rustyboy21 Posts: 2,565 Forumite
    How long has boiler been fitted?

    Don't think it would be the wind, otherwise loads of other people would be having the same problem. It sounds like it could be low gas pressure on firing. You may find that the main run of gas pipe is ok, but the engineer may have reduced the diameter closer to the boiler. As Karl said, the initial 'pilot light' ( I know it is electronic ignition, but it will need something to light the rest of the burners) could be lighting, but the pressure goes down on gas being let out into the burners, so therefore it cuts out.

    I know a fair bit about fires, but only general on boilers, but Karl..... Is it usual practice to check gas pressures at meter and boiler when servicing a boiler? If the engineer just cleaned it out and not checked the pressures, it could be that the gas co has been work and your pressure has changed. Maybe worthwhile getting gas co out to check pressure into house. Otherwise get a ' better' engineer in to check boiler out
  • gas4you
    gas4you Posts: 2,602 Forumite
    edited 2 December 2011 at 8:46PM
    I doubt it is anything to do with the wind. Will be gas related. Get a different gas engineer in to look at it?

    I always check gas pressures ( working pressure) at the meter on a service, as well as doing a tightness test. I know it is not a legal requirement, but how would one know an installation is safe and working properly without doing these very basic tests?
  • karl-123
    karl-123 Posts: 360 Forumite
    if the ignition/electrode is burnt away
    as canuckhead has said in earlier posts

    that could cause misfiring as the electrode
    wont pick up heat in high winds
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    how much would getting the gas pipework sizing sorted roughly ?


    Sooooo, getting down to the nitty gritty then.

    Any other problems with the installation?

    Only an RGI can tell you what you ask, it's calculated out according to the property, not as a 'rule of thumb'

    I cannot see why a properly installed boiler would suffer from wind!!:)

    GSR
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • karl-123
    karl-123 Posts: 360 Forumite
    edited 2 December 2011 at 9:28PM
    at the end of the day
    the boiler could be absolutely fine :j

    but the high winds playing on the fan :mad:
    could simply cause the diaphragm not to engage permanently
    in the air pressure switch :mad:
    therefore the double pole switch contacts consisting of
    common ( live ) normally closed, and normally open in the air pressure switch which are switched ,live back, from the relays on the pcb,
    after the fan is proved for safety do not reamain closed/on

    " i cannot train you i,i can only show you the way"
    bruce lee ...........
    pps.........22mm gas pipework to the boiler is the norm
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.3K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.2K Work, Benefits & Business
  • 603.9K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.