Boiler losing water pressure

Options
ian-d
ian-d Posts: 371 Forumite
I have a Potterton Powermax HE (150ltr) boiler (approx. 5 years old) which appears to be losing water pressure quite quickly.

I was originally told that topping up the water pressure via the value is quite normal once or twice a year, but I noticed yesterday that the boiler was on lock-out and after topping up to 1.5, it is back down to 0.9 today.

Would this suggest a leak? Anything easy I can test prior to having to get someone in?
«13

Comments

  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Is it leaking via the PRV? Have a look outside.
    No free lunch, and no free laptop ;)
  • ian-d
    ian-d Posts: 371 Forumite
    Nope, seems fine. Next door seem to have always had a drip of water coming out of theirs but ours has never done the same.
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Then it must be leaking elsewhere on the CH circuit unfortunately.
    No free lunch, and no free laptop ;)
  • gas4you
    gas4you Posts: 2,602 Forumite
    More than likely the expansion vessel is flat or knackered. This is extremely common on these. I look after loads of these and all have had to have the expansion vessel replaced after about 4-5 years.
  • Yorkie1
    Yorkie1 Posts: 12,014 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Combo Breaker
    gas4you wrote: »
    More than likely the expansion vessel is flat or knackered. This is extremely common on these. I look after loads of these and all have had to have the expansion vessel replaced after about 4-5 years.

    Would you say Baxi105e boilers have similar issues with the expansion vessel, gas4you?
  • ian-d
    ian-d Posts: 371 Forumite
    Oddly the pressure is now showing 1.4/1.5 without a top up, rising to 2.0 when running/warming the house, so weird how it was 0.9 this morning then back up again! Is topping up quite normal at least a couple of times a year?

    Just in case, where is the expansion vessel located?
  • gas4you
    gas4you Posts: 2,602 Forumite
    Op. yes topping up 2 or 3 times a year is quite normal. The expansion vessel is inside the top right of the boiler. The grey metal vessel. Easy access and you don't have to disturb any seals or gas parts to get to it.

    Yorkie1. Yes it could also be a fault with the 105e EV, but not to such a common extent. It is a different EV on the 105e and not prone to faulting so often.
  • ian-d wrote: »
    Would this suggest a leak? Anything easy I can test prior to having to get someone in?
    It doesn't suggest a leak, it proves it.
    Look for water where it shouldn't be.
  • ian-d
    ian-d Posts: 371 Forumite
    Just a follow up to this, the water pressure hasn't reduced much since topping it up, so possibly needs doing every 2-3 months. However, I've noticed that when the boiler isn't in use, it is set to about 1.5, yet when the boiler is running, it reaches 2.5. Is it normal for the pressure to increase?
  • SYNERGY
    SYNERGY Posts: 129 Forumite
    ian-d wrote: »
    Just a follow up to this, the water pressure hasn't reduced much since topping it up, so possibly needs doing every 2-3 months. However, I've noticed that when the boiler isn't in use, it is set to about 1.5, yet when the boiler is running, it reaches 2.5. Is it normal for the pressure to increase?

    Yes the pressure increase is normal and due to the expansion of the water in the CH circuit when heated.

    The extra volume of water is taken up by the expansion vessel

    As a matter of interest, if you set the boiler pressure when the system was slightly warm (whole house at 15deg ) to say 1bar, the CH wasn't used for the next day, the temperature in the house dropped to say 5deg then you would see the pressure drop to below 1bar due to the colder water taking up a lower volume in the system.

    Just wondering if you have set the pressure slightly too high at 1.5bar ?

    Most systems are 1bar when cold.

    You say that when hot it is 2.5bar, this is not a problem in itself but at 2.5 bar it is approaching the lift off pressure of the pressure release valve at 3bar.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.