wiring up a ceiling light too many wires!! HELP!!

Hi All.
PLEASE HELP!!
I bought a light for my son's bedroom but when i detached the old light i found, to my horror, 6 wires rather than the expected 2!
Coming out of the ceiling there are 2 cables and in each are a red, black and yellow/green cables (6 in total) and the light that i have bought to go up there has access for a blue and a brown wire!

do i wind together the reds and put them to the brown and then wire together the blacks and put them to the blue???? what about the yellow/green?

Any help appreciated.

Thanks,

Sancho.

Comments

  • Hi,

    you might get some help in these threads.

    Look1

    Look2.
  • ormus
    ormus Posts: 42,714 Forumite
    1zogpdx.jpg

    old colors.
    just substitute red to brown and black to blue, if required.

    ps.
    note the switched live wire. it should have a (red) marker on the end. as shown.
    Get some gorm.
  • googler
    googler Posts: 16,103 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Combo Breaker
    If the reds are wound together at one terminal at the moment, and if the black and yell/green are the same, then I'd be inclined to say leave them that way - get a terminal block, attach them to the terminal block the same way, and take blue from the black and brown from the red on the other side of the terminal block. Are the reds currently attached to a terminal marked positive or +ve on the existing light? Are the blacks all attached to negative or -ve? Are the yell/green all attached to a terminal with the universal earth symbol?

    Don't assume because you've switched off at the lightswitch that the cables are dead - switch off the whole lighting circuit at the fusebox or consumer unit.

    If you don't know what a terminal block is, or are stumped by this level of wiring complexity, should you really be doing this? Is it time to call an electrician?
  • googler wrote: »

    If you don't know what a terminal block is, or are stumped by this level of wiring complexity, should you really be doing this? Is it time to call an electrician?

    I agree with what you write. The OP is just asking for trouble. Messing up the wiring could invalidate the house insurance as well :eek:
    I used to have a signature but it disappeared and I just couldn't be bothered writing another, so please feel free to ignore this.
  • DVardysShadow
    DVardysShadow Posts: 18,949 Forumite
    Judge it by what goes into the old lamp. Regardless of what comes out of the ceiling, there will only be 2 connections into the old lamp, plus an earth [green/yellow]. Provide you maintain the right wires into the connections on the new lamp you will be fine. Oops, you got impatient and disconnected the lot? Then you will have to understand the wiring and sort it from first principles.
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam
  • ormus
    ormus Posts: 42,714 Forumite
    afaq38.jpg

    ive omitted the lamps from this one. for clarity. and named the four connections.
    your two lamp wires go to N2 and SL4.

    normal prctice is black (or blue) to N2, and red (or brown) to SL4.
    (they can go either way round).

    earth is (usually) only required for metal lamp fittings.

    if you havent got a ceiling rose, then you will need some terminal/connecting blocks.
    Get some gorm.
  • keystone
    keystone Posts: 10,916 Forumite
    edited 28 August 2011 at 4:56PM
    Dvardy is correct. Did you oberve carefully what wires went where in the old light?

    Did the old light have one of these:

    38618.jpg

    If it did the wiring inside would look like this:

    ceiling_rose.jpg


    As you say there are only two cables it will be the end of the run so the cable on the upper RHS will not exist (as Ormus diagram shows that is taking the power onto the next lamp on the circuit) so we can ignore it.

    You need to identify which is the "switched" live. Thats the one on the lower RHS of this picture. As you can see the reds from both cables are connected together. The black from the supply cable is connected to the connector to whioch the blue from the fitting connects. The switched live black where it arrives from the switch itself should be sleeved with a red sleeve to indicate that its live and that connects to the brown wire from the fitting.

    It sounds as though you may have removed the rose [STRIKE]thing[/STRIKE] thinking its part of the whole light fitting itself which it isn't. Was your old light like this:

    light_fitting.jpg

    If your new fitting is a pendant light (like the one above) with just a length of flex containing blue and brown conductors then you need to replace the rose and then reconnect as shown.

    If, however, the new fitting doesn't require a rose (which it may not if its a fitting like this:

    Magnum3_Spot.jpg

    then we have another situation and as googler says you'll have to replicate the connections in the rose by another means.

    So first things first. Does the new light not need a ceiling rose? Can you upload/post a pic of the underside of the new fitting?

    Whatever you do, as already advised and in all circumstances, make sure that the complete lighting circuit is off and totally dead beforte you touch anything else as the supply cable will remain live even though the switch is off.

    If the above doesn't make immediate sense to you then you should get someone in to look at it for you.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • DVardysShadow
    DVardysShadow Posts: 18,949 Forumite
    keystone wrote: »
    light_fitting.jpg
    UltimateHandyMan .co .uk make Ultimate Numpties of themselves :rotfl::rotfl::rotfl:
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam
  • 27col
    27col Posts: 6,554 Forumite
    The mere fact that the op took the wires out without noting where they were connected should ring alarm bells as to his ability to do the job safely. If you can read the diagrams that have been helpfully posted by ormus and keystone then have a go, if not, then keep well clear.
    I can afford anything that I want.
    Just so long as I don't want much.
  • keystone
    keystone Posts: 10,916 Forumite
    UltimateHandyMan .co .uk make Ultimate Numpties of themselves :rotfl::rotfl::rotfl:
    T'was the first picture that came up on search showing a complete pendant fitting and rose. didn't really look at the url and don't really care actually (:p) but you'm right anyway.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.5K Banking & Borrowing
  • 252.9K Reduce Debt & Boost Income
  • 453.3K Spending & Discounts
  • 243.5K Work, Benefits & Business
  • 598.2K Mortgages, Homes & Bills
  • 176.7K Life & Family
  • 256.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.