No hot water from boiler? any help?

2»

Comments

  • plumb1_2
    plumb1_2 Posts: 4,640 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    ^opm^ wrote:
    as a side thought i have my central heating disconnected at mo and drained down and a radiator off wall as im decorating-but cant think this affects this as i have done this before and still had hot water but this morning pipes woke me up making a gurgling noise-could this somehow have put an airlock in system?

    Your problem was that you have drained down the system, with no water in the system the boiler will light up and the boiler stat will sense the temp and shut down. What you did by draining the system and trying to fire/light the boiler up again was VERY DANGEROUS:naughty:, as if you had a faulty stat, you will have had your boiler flying off the wall and passing through the window/wall. And ruin the seals on the boiler
    A bit like turning a kettle on with no water in it and no trip cutoff switch.
    A thankyou is payment enough .
  • ^opm^
    ^opm^ Posts: 164 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    oops-think i wont apply for a plumbing job then lol-thanks for help everyone tho
  • Martini
    Martini Posts: 607 Forumite
    Part of the Furniture Photogenic Combo Breaker
    ^opm^ wrote:
    as a side thought I have my central heating disconnected at mo and drained down and a radiator off wall as I'm decorating-but cant think this affects this as I have done this before and still had hot water but this morning pipes woke me up making a gurgling noise-could this somehow have put an airlock in system?

    Hmm,
    As Plumb1 stated not a very good idea at all!
    Don't use the boiler to heat your water if you are draining down parts of your sytem for maintanance! It is okay if you remove a radiator by isolating its valves but not when draining down either partially or completely! You obviously have air in the pipes and its not good for the pump or the boiler to run. Your boiler was shutting off on its "overtemperature" thermostat as the small amount of water in it wasn't moving anywhere and it boils in seconds!
    Don't do this again as you could blow your boiler up!
    Keep Smiling
    :) Site member number 24 :)
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.2K Banking & Borrowing
  • 254.3K Reduce Debt & Boost Income
  • 455.3K Spending & Discounts
  • 247.2K Work, Benefits & Business
  • 603.8K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.3K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.