Boiler pressure queries

worcester bosch 25si problem

boiler approx 6 years old and had heat exchanger replaced a few years ago.

operating at approx 2.5 - 3 bar (should be between 1 - 2.5)

heating and water coming on but hearing boiler firing-up approx every 5-10mins

when switched off pressure going to below 1 within 1 hour so not sure what it is when it switches on in the morning but would not be surprised if it is at 0!

checked all radiators and no leaks , cold bits and have all been bled.

no water leaking from pipe outside

At a total loss to what it is and dont want to leave it in case it turns into something serious!

Have heard people talking about filling air back into system via a bicycle pump?

Any help would be gratefully received!

As I am a student cant afford to pay out for something unless totally necessary.

HELP!!!!!!!!!!!!!!!!!!!!!!!!

Comments

  • Good morning: Possibilities include filling loop letting by or perforated heat exchanger.

    HTH

    Canucklehead
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • lrr_2
    lrr_2 Posts: 945 Forumite
    If filling loop was staying open would the pressure not stay up when switched off instead of dropping? Surely I cant be needing another heat exchanger? Last one was just replaced approx 4 years ago.
  • lrr_2
    lrr_2 Posts: 945 Forumite
    I thought possible pressure release valve not opening and closing properly?
  • Hi..Take a look at these FAQs ....if you can't find the answer, then post your query on the DIYnot plumbing & heating forum.

    You're welcome;)

    HTH

    Canucklehead
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • lrr_2
    lrr_2 Posts: 945 Forumite
    thanks for the help.
    looks like its the pressure vessel needing re pressurised

    is this easy to do?

    found the nossle for cycle pump
  • lrr_2
    lrr_2 Posts: 945 Forumite
    Just an update

    Repressurised the expansion vessel myself and working like a dream now!

    Probably just saved myself a fortune on a plummer!
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 353.6K Banking & Borrowing
  • 254.2K Reduce Debt & Boost Income
  • 455.1K Spending & Discounts
  • 246.7K Work, Benefits & Business
  • 603.1K Mortgages, Homes & Bills
  • 178.1K Life & Family
  • 260.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.