Economy 7 again....

Options
Hello there.

Sorry if this has already been posted somewhere. I can find lots of posts about economy 7 but not answering this specifically...

Today I am having storage heaters put in. The electrician is going to install a new fuse box so that they are on a separate night circuit.

We also have a cylinder to heat out hot water. this has got two heating element with two separate inputs which are on timers.

So far we have not been on a economy sever meter so I just want to check I have this right....

I have been told that to take advantage of the economy 7 tariff the hot water cylinder needs to be wired to the off-peak fuse board (where the heaters will be wired)? Is this correct? I assumed that because it has timers that if I set them up to come on at night only we would automatically make use of the cheaper electricity.

This bring me to ask something else: does this also mean that any appliances which we would like to use of the off peak energy (washing machine etc..) would have to be wired in onto that same circuit.
I assumed that all of the house's electricity would be cheap at night but maybe that is not the case....

any advise welcome.

Thanks

Comments

  • jolou
    jolou Posts: 55 Forumite
    Have you read my post here http://forums.moneysavingexpert.com/showthread.html?t=1184559.
    It sounds like what you are talking about. I am trying to find out if it is possible to have everything put onto the economy 7 circuit.
  • Thanks Jolou,

    It does look like we are asking the same thing. Have you managed to find out the answer to your questions yet?
    I was originally told that it very much depends on the type of meter which is installed.
    As mine is yet to be installed I would apprciate if anyone knows so that I get it right....

    Thanks
  • Rikki
    Rikki Posts: 21,625 Forumite
    I have economy 7 but don't have storage heaters. I use timers to take advantage of the cheap night time electricity.
    £2 Coins Savings Club 2012 is £4 :).............................NCFC member No: 00005.........

    ......................................................................TCNC member No: 00008
    NPFM 21
  • Premier_2
    Premier_2 Posts: 15,141 Forumite
    10,000 Posts Combo Breaker
    If you have the immersion heater connected to the off peak supply only, you won't be able to heat water during the day.

    Better to have the immersion heater on a time switch that takes advantage of the low rate period, but which you can then over-ride if you need more hot water during the day.

    All electricity used during the low rate period will be priced at the low rate. The only advantages of having appliances on a specific low rate circuit is that (a) you don't need a separate timer for them and (b) you are guaranteed to only use then during the off rate period. A separate timer may not be adjusted to suit the actual period you are obtaining low rate electricity, but a low rate circuit will automatically switch on when the low rate is active (whatever time that happens to actually be).
    "Now to trolling as a concept. .... Personally, I've always found it a little sad that people choose to spend such a large proportion of their lives in this way but they do, and we have to deal with it." - MSE Forum Manager 6th July 2010
  • Premier wrote: »
    If you have the immersion heater connected to the off peak supply only, you won't be able to heat water during the day.

    Better to have the immersion heater on a time switch that takes advantage of the low rate period, but which you can then over-ride if you need more hot water during the day.

    All electricity used during the low rate period will be priced at the low rate. The only advantages of having appliances on a specific low rate circuit is that (a) you don't need a separate timer for them and (b) you are guaranteed to only use then during the off rate period. A separate timer may not be adjusted to suit the actual period you are obtaining low rate electricity, but a low rate circuit will automatically switch on when the low rate is active (whatever time that happens to actually be).

    Thanks Premier. that's great news and it is reasuring.
    we have two heating elements on the boiler so would youi say it would make sense to have one connected to the off-peak circuit and one to the normal circuit (which we would only switch on when necessary). or shall I leave it as it is as both elements are on a timer already?
  • Ada3050
    Ada3050 Posts: 227 Forumite
    Car Insurance Carver! Cashback Cashier
    You should connect the lower heating element to the economy 7 circuit and the other one to the day time circuit, then you can boost the top half of water in the day time.
    Know the difference between what you WANT and what you NEED. :T
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.