Trying to optimise my Valliant ASHP

2

Comments

  • QrizB
    QrizB Posts: 25,683
    10,000 Posts Fifth Anniversary Photogenic Name Dropper
    Forumite

    If you want to use a heat pump to supply heat quickly you need to set the leaving water temperature to be high, which will cause the heat pump to run less economically that it could (which in itself might be okay if electricity is cheap).

    Yes, I think the idea is that most people don't care as much about how much energy they use, and more about what it costs. Getting a COP of 3 at 15p/kWh is cheaper overall than a COP of 4 at 25p/kWh.

    But I'm not aware of any heat pump that lets you set the LWT to different temperatures at different times of the day

    Doesn't your compensation curve do that? So by setting back the room thermostat, you'll decrease the LWT? (And, depending on how the room temperature holds up, you might not get a call for heat at all during the setback period.)

    N. Hampshire, he/him. Octopus Intelligent Go elec / Fuse gas / Vodafone BB / iD mobile. Kirk Hill Co-op member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 37 MWh generated, long-term average 2.6 Os.
    Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Ecoflow Stream, Best kettle :-)
  • Reed_Richards
    Reed_Richards Posts: 5,960
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    Forumite

    My new electricity supplier has gifted me a few hours of free electricity. During that time I could set my Leaving Water Temperature to the maximum that my heat pump is capable of and the thermostatic control to some unobtainably high value and that would force my heat pump to work as hard as it is capable of (albeit inefficiently). I don't need my heat pump to be over-specified but I would need to manually override the normal controls. Maybe the Octopus Cosy Heat Pump can be set to do this on a predetermined schedule, but most heat pumps can't.

    Reed
  • Magnitio
    Magnitio Posts: 1,387
    Fifth Anniversary 1,000 Posts Name Dropper
    Forumite

    @frankiesowner

    I had a new Vaillant installed earlier this year. I read a lot of advice from people about leaving it running 24/7 on "low and slow". This is great for efficiency, but not necessarily overall cost. The new Vaillant heat pumps are very efficient and the controls are good at adjusting the flow temps to help you reach or maintain your target. You can increase the target temperature during cheap rate and decrease it when it's expensive. It works very well. The only issue can be heating hot water and the house during one of those cheap periods, especially if you use a lot of hot water or have a small cylinder.

    We are on Octopus IOG tariff which provides very cheap electricity 23:30 to 5:30 (6.6p/kWh) but very expensive for the rest of the day (35.89p). We also have solar and a 10kWh battery that we charge overnight. Our schedule is:

    Hot water cylinder 23:30 - 1:30 (although it often finishes earlier)

    1:00 - 5:30 - 22C (our bedrooms are cooler, but this puts some heat into the structure of the house)

    10:00 - 20:00 - 20C

    Setback temp of 19C

    So far this heating season we haven't had a day where we have run out of battery and with a COP of 5 this month, it's been very cheap to run.

    That's our experience based on the structure, heat loss and usage of our house. Yours may well be different.

    6.4kWp (16 * 400Wp REC Alpha) facing ESE + 5kW Huawei inverter + 10kWh Huawei battery. Vaillant Arotherm Pro 7kW heat pump.
  • Thanks for all the helpful replies. I won't say I understand every one BUT I am researching the concepts that people have raised. In the meantime I've decided to go for a new fixed rate contract with one tariff since I have to make a decision now to 'lock in' the possibly cheaper tariff. Granted in the OP I mentioned my keenness to explore the variable tariffs from the likes of Octopus but two things; first I don't have solar/battery and would be dependent on the higher tariff during the day and second I'm not sure as a household we could 'adapt' to the discipline needed to exploit the variable tariffs (cheaper windows throughout the 24 hrs). In the meantime I'm looking into how to get the system settings right to get the right 'heat curve' (thanks for the input MWT ).

  • mk321123
    mk321123 Posts: 11
    10 Posts
    Forumite

    A fixed rate makes it simpler: with one price all day there's nothing to gain from running it in bursts, so leave it on all day at one room temperature, no setback, and let the curve do the work.

    The step by step you asked for, one change at a time:

    • Open every TRV fully, like Netexporter said, and leave the main thermostat on one steady temperature day and night.
    • Lower the heat curve one small step. If the rooms still hold their temperature comfortably for a day or two, go another step down.
    • When a room starts to feel cold, go back up a step and leave it there for a few days. Write down the outdoor temperature each day as you go, otherwise you can't tell whether the curve or the weather made the difference.
    • Check again in the next cold spell. A curve that's fine at 10 °C outside can fall short at 0 °C. Then raise the curve a little rather than turning the thermostat up.

    If one room always lags while the rest are fine, that's a balancing job for that radiator (close the lockshields on the others a little), not a reason to raise the whole curve. MWT's energy-stats link explains what the curve numbers mean on the Vaillant.

    It takes a few weeks of checking, but once it's tuned the lowest curve that still keeps you warm is also the cheapest way to run it.

  • Magnitio
    Magnitio Posts: 1,387
    Fifth Anniversary 1,000 Posts Name Dropper
    Forumite

    There may be nothing to gain in terms of overall energy usage, but there is in cost.

    6.4kWp (16 * 400Wp REC Alpha) facing ESE + 5kW Huawei inverter + 10kWh Huawei battery. Vaillant Arotherm Pro 7kW heat pump.
  • Reed_Richards
    Reed_Richards Posts: 5,960
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    Forumite

    Open every TRV fully, like Netexporter said, and leave the main thermostat on one steady temperature day and night.

    Hang on, what @Netexporter actually said, which is the correct advice, was:

    you will get a better SCOP if you open them all fully and balance each radiator with the valve on the other end of the radiator.

    Balancing using the valve is very important!

    Reed
  • Netexporter
    Netexporter Posts: 3,173
    1,000 Posts Third Anniversary Name Dropper
    Forumite

    On balancing radiators, I have found that using a thermal imaging camera is a very easy way to ensure your return temperatures are as low as possible. I also have a 2-channel thermometer that reads the inflow and outflow temperatures and thus the delta-t but the visual method afforded by the camera correlates very well (and the colours are pretty!).

    When balancing I completely close the balance valve then open it half a turn and check results. I then open the valve, if necessary in quarter turn increments, until a satisfactory flow results. It is surprising how little the valve generally needs to be open.

    With the camera you want to aim to have the red zone to about three quarters of the way down the radiator with a clear cool zone right across the bottom of the radiator.

  • michaels
    michaels Posts: 29,813
    Part of the Furniture 10,000 Posts Photogenic Name Dropper
    Forumite
    edited 26 November at 7:00PM

    With the valiant can you adjust the level and the gradient separately?

    Our LG is not very user-friendly but basically you set a min outside air temp and associated flow temp.and same for max and the curve is a straight line between the two.

    I think....
  • MWT
    MWT Posts: 11,335
    10,000 Posts Sixth Anniversary Name Dropper
    Forumite

    Vaillant uses the desired temperature target to set the level and you adjust the gradient separately.

★ ★ ★ Meet your Ambassadors

Categories

  • All Categories
  • 356K Banking & Borrowing
  • 255K Reduce Debt & Boost Income
  • 456.3K Spending & Discounts
  • 248.5K Work, Benefits & Business
  • 606.3K Mortgages, Homes & Bills
  • 179.1K Life & Family
  • 264.1K Travel & Transport
  • 1.6M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards
Quick Search

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.