One radiator not heating issue

Hi

Im having an issue with a radiator, i thought it was broken but before getting someone out to check thought i would do some testing.  The front room radiator was not getting hot, im not sure how long it was like this and only really noticed after having boiler replaced for a slightly bigger version with a higher flow rate.

There was a slight, very slight heat at the top but thats all.  Today i have done some testing.  With the boiler on and the rest of the rads hot, there was no heat from the pipes going to either the trv or lockshield valves.  I turned all the other rads off with their valves and the front room rad started heating up and is now roasting, to the point i dont want to keep my hand on it, the pipe to the lockshield is also very hot and the pipe to the trv is hotter but not as hot.  So it would seem like the rad is fine but not when the others are switched on.  The others being off is not a big deal but id like two of them on, 1 can stay off.  Im turning the others that i want on every 20mins or so to see what happens.

Anyone any idea why the front room would only get hot when others are off?

Comments

  • It may be that your system needs balancing?
  • plumb1_2
    plumb1_2 Posts: 4,671
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    Forumite
    Ya need’s balancing, close all the lockshields off then gradually open them up. Quater turn each time.
    Start the furthest away from the boiler
    A thankyou is payment enough .
  • cheers guys.  Ill look into it but i hate dealing with water.  I may get a professional in.
  • CliveOfIndia
    CliveOfIndia Posts: 2,952
    1,000 Posts Third Anniversary Name Dropper
    Forumite
    cheers guys.  Ill look into it but i hate dealing with water.  I may get a professional in.
    Balancing a heating system is actually very straightforward - if you search online, you'll find dozens of guides on how to do it, and you don't need any special equipment apart from a thermometer.
    It is, however, extremely tedious and time-consuming.  If you're able to have a bash at it yourself you'll likely save yourself a fair amount - a plumber/heating engineer will have to charge quite a lot, purely because of the length of time it takes.

  • IvyFlood
    IvyFlood Posts: 365
    Eighth Anniversary 100 Posts Name Dropper
    Forumite
    edited 2 March 2023 at 4:04PM
    We had one radiator like this in our botched extension which turned out to be furthest away from the boiler. We had our system drained and pipework replaced when we got a new boiler in 2020. The guy had to go under our house to do it as not to disturb our wood flooring, he said it was like spaghetti junction under there! Said radiator now gets piping hot
★ ★ ★ Meet your Ambassadors

Categories

  • All Categories
  • 356K Banking & Borrowing
  • 255K Reduce Debt & Boost Income
  • 456.3K Spending & Discounts
  • 248.5K Work, Benefits & Business
  • 606.3K Mortgages, Homes & Bills
  • 179.1K Life & Family
  • 264.1K Travel & Transport
  • 1.6M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards
Quick Search

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.