Ready, steady… save!
You don’t need a chart to join in. Here are 2 ways to record your savings:
1. Cross it off
Pop a chart into your first post. Saved an amount? Cross it out! Read more »
£0.01 £0.02 £0.03
2. Write it down
Skip the chart and add updates to your first post. Read more »
“Another +£3 saved today. Go me!”
Use +£ before each new saving so it counts towards your total.
We’d like to remind Forumites to please avoid political debate on the Forum.
This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.
Home energy efficiency consultancy service
Comments
-
It will turn off when turned to 2 because the room is already warmer than whatever temperature "2" is for that TRV. If you close the door and leave the room to cool for a while, the TRV will open the valve once the room temperature drops to around 15C on setting 2.
As I previously said, the TRV does not change the temperature of the radiator. It simply closes the valve so the water no longer flows through the radiator once the room has reached a set temperature.
The only way to alter how hot the water flow is, is by changing the settings on the boiler. If your radiators are extremely hot then the boiler flow temperature should be set lower. Most boilers have either a digital display showing the temperature (set it to 50-60C) or a dial which can lower it. Condensing boilers run more efficiently if the flow temperature is around 50C.Barnsley, South Yorkshire
Solar PV 5.25kWp SW facing (14 x 375) installed Mar 22
Lux 3.6kw hybrid inverter and 9.6kw Pylontech batteries
Daikin 8kW ASHP installed Jan 25
Octopus Cosy/Fixed Outgoing
Kia EV63 -
Alnat1 said: Condensing boilers run more efficiently if the flow temperature is around 50C.More precisely, it is the return temperature that should be less than 54°C to ensure the boiler is condensing. This means that your flow temperature coming out of the boiler could be 10-12°C higher.
Any language construct that forces such insanity in this case should be abandoned without regrets. –
Erik Aronesty, 2014
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.0 -
LV_426 said:Alnat1 said:What is the number on the TRV set to? The number relates to the approximate temperature the room will get to before the TRV closes the flow. TRVs can't adjust the water temperature or adjust the flow rate, that isn't how they work.
For a bedroom a setting of 2 might be ok, somewhere around 15C a setting of 3 might give you around 20C. It will vary a bit depending on radiator and room sizes. You will need to keep the bedroom door closed too.
Well let me give you an example of one rad I've been experimenting with. Dial has 4 settings (1 - 4). If you set it to 3, the rad gets melting hot. Shift it a tiny amount towards 2, and it shuts off completely, no heat. So there's apparently no middle ground, it's either on or off. This is why I find them practically useless.That is what radiators do. Simplifying rather, they are either letting hot water from the boiler into them, in which case they are at the temperature of the hot water set by the boiler. Or they aren't letting hot water in, and cool down. The only middle ground is when a radiator valve has recently shut off and the radiator is slowly cooling down. There is no way for a radiator to be on and at any temperature other than the hot water from the boiler (minus losses in the pipework). The radiators should switch between on and time off depending on the room temperature. You can of course change the boiler temperature setting which will cool down all the radiators.But a banker, engaged at enormous expense,Had the whole of their cash in his care.
Lewis Carroll0 -
i'm wondering if theres some cross talking here?
thermostats work (when they work) by having the heating on until they detect a temp then turning the heating off. they then stay off until the heating is below the temp. that can be at the boiler or at the radiator depending which thermostat we're talking about.
so the op could be saying that setting the thermostat to 2 keeps the rad off constantly (when the room and rad is cold). but having it set at 3 and the rad/room warms up. and that would mean a faulty valve.
or they could be saying the rad heats at three. and doesn't turn off unless they turn it down to 2. which could be that its not getting hot enough to turn off at 3 but is hotter than 2. possibly an insulation or boiler flow temp problem or it could mean a faulty valve.
or they could be saying the rad gets hot at 3 and turns off when they turn it down to 2. which would be working as its supposed to as the rad wont turn back on in that situation until the temp has dropped enough to be below the 2 temp.
it would be great if the op could confirm which of those is right (or if none of them are and i've completely lost the plot).Almost everything will work again if you unplug it for a few minutes, including you. Anne Lamott
It's amazing how those with a can-do attitude and willingness to 'pitch in and work' get all the luck, isn't it?
Please consider buying some pet food and giving it to your local food bank collection or animal charity. Animals aren't to blame for the cost of living crisis.0 -
Is the not marks between the numbers, you don't just use the numbers, every millimeter or 2 will be a degree depending on the spacing an the start and end points, 8c - 26c
0 -
ariarnia said:i'm wondering if theres some cross talking here?
thermostats work (when they work) by having the heating on until they detect a temp then turning the heating off. they then stay off until the heating is below the temp. that can be at the boiler or at the radiator depending which thermostat we're talking about.
so the op could be saying that setting the thermostat to 2 keeps the rad off constantly (when the room and rad is cold). but having it set at 3 and the rad/room warms up. and that would mean a faulty valve.
Yes this is exactly what I'm saying.
I understand that the valve should be reacting to the ambient temperature, depending on where the control dial is set to.
However when set to 2, I get no heat at all in the radiator, and the room gets progressively colder.
It's not the only rad in the house that behaves this way. So I think my best plan of action would be to purchase a new set of quality TRVs for the house.
1 -
markin said:Is the not marks between the numbers, you don't just use the numbers, every millimeter or 2 will be a degree depending on the spacing an the start and end points, 8c - 26c
If the tolerance is down to millimeter precision, then what's the point of the numbers on the dial being so far apart? The scale seems wrong, and should be much finer. A couple of degrees difference in heat is quite noticeable.
0 -
you can buy digital ones that you can set precisely but the difference between the numbers is about 5 degrees.LV_426 said:markin said:Is the not marks between the numbers, you don't just use the numbers, every millimeter or 2 will be a degree depending on the spacing an the start and end points, 8c - 26c
If the tolerance is down to millimeter precision, then what's the point of the numbers on the dial being so far apart? The scale seems wrong, and should be much finer. A couple of degrees difference in heat is quite noticeable.
also worth remembering that if the radiator is on one side of the room then the thermostatic valve is on the rad. a big room and there might be a few degrees difference from next to the rad to the other side anyway so its not a precise science.
so you need to play around and find the number that works for that room with that size and air flow. if the valve is set to somewhere between 2 and 3 it should be about 17-18 degrees.Almost everything will work again if you unplug it for a few minutes, including you. Anne Lamott
It's amazing how those with a can-do attitude and willingness to 'pitch in and work' get all the luck, isn't it?
Please consider buying some pet food and giving it to your local food bank collection or animal charity. Animals aren't to blame for the cost of living crisis.0 -
I had all my trvs changed last year to a Danfoss model that does automatic balancing (RasB2). These are a game changer for me. Full control over a room and everything balanced. All the lockshields are set to open and the balancing is done at the trv body via an app).LV_426 said:So I think my best plan of action would be to purchase a new set of quality TRVs for the house.2 -
Something the OP should check is whether the TRVs are fitted to the incoming flow or the outgoing return side of the radiators. If fitted to the return side it is possible that the pressure of flow through the radiator pushes the valve down (against the spring loading) and shuts the radiator off prematurely.1
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards



