electric showers
pingu79
Posts: 66 Forumite
Hi,
just bought my 1st house, and the shower doesn't work at all. How easy is it to install a new electric shower. Can i do this now with part P regs???
Thanks
just bought my 1st house, and the shower doesn't work at all. How easy is it to install a new electric shower. Can i do this now with part P regs???
Thanks
0
Comments
-
Hi,
just bought my 1st house, and the shower doesn't work at all. How easy is it to install a new electric shower. Can i do this now with part P regs???
Thanks
Are you sure that there is not an isolation switch or water valve that needs to be turned on?
It's easy to replace a shower if you know how but that fact that you are asking suggests that you wouldn't have a clue what to do! Most jobs are easy if you know how and have the correct tools. Repairs, replacements and
maintenance work is excluded from Part P.:doh: Blue text on this forum usually signifies hyperlinks, so click on them!..:wall:0 -
Hi,
just bought my 1st house, and the shower doesn't work at all. How easy is it to install a new electric shower. Can i do this now with part P regs???
Thanks
Yes, its very easy and if you are doing a straight replacement it doesn't come under part p regs. I advise getting a replacement shower that is the same make as the one you currently have so the water inlet and wiring terminal are in the same place - this will make the job a lot easier.0 -
don't buy a gainsborough- they are sheeeeet.
triton are good, mira are ok.
(this is my opinion)baldly going on...0 -
Sorry,
should have expanded on my original post.
The current heating system has a fan assissted bolier with cast iron heat exchanger. The hot water tank is at 1st floor level in the airing cupboard, with the cold tank above (below ceiling level).
The current shower is run off the heating system, with a twin impeller pump. However looking at the installation reccomendations for the pump type, the water level in the cold tank should be 9 inches below the shower head. it isn't the pipes feeding the shower are about 9 inches above the water level in the cold tank. So would this ever have worked or has it been put in incorrectly in the 1st case? We raised this with the vendor after we moved in and heard nothing back, which to my mind seems kind of damning.
My partners brother is in the trade and reckons that even if we moved the cold tank to the correct level the size of the hot water cylinder would only provide about 5-6 mins of hot water.
I have checked all the valves to make sure and they are all in the correct position.
Therefore as a replacement I was thinking about installing an electric shower instead. Yes my DIY skills aren;t fantastic at the mo, as its my 1st house but, have relatives who are pretty good who would lend a hand.0 -
Yes, this setup sounds wrong. Presumably the cold water tank is quite small with it being in the location it is. Usually a 50 gallon cold water tank is recommended to avoid pumping the tank dry which could damage the pump.
Basically you would have to install a dedicated electrical supply with the appropriate RCD and circuit breaker. You could do this yourself but it would come under the dreaded part P so you would have to get it signed off by an appropriate person. If your not confident in your ability it is probably best to get someone in.
Plumbing in the water feed should be quite straight forward - you just need to take a cold feed from the mains supply. Again, if you arent confident in your DIY skills it might be better to get someone in rather than risk a leak.0 -
If you are doing a swap please make sure it is the same kW as the previous one or get someone to check if the cable can cope. If you get one with a higher rating you might burn the cable out.:cool:
"You have enemies? Good. That means you've stood up for something, sometime in your life." Winston Churchill
[SIZE=-1]
[/SIZE]0 -
Could you not just raise the cold tank to get the water levels right?
I have to say the set up you've got would work brilliantly if it was properly installed.Behind every great man is a good womanBeside this ordinary man is a great woman£2 savings jar - now at £3.42:rotfl:0 -
sounds like the old system would never work properly.
fit the new lecky shower yourself (plumbing etc.) and get a sparks to wire it up for you.Get some gorm.0
This discussion has been closed.
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards