trouble sourcing an old circuit breaker...any ideas please?

Hi all,
(If you don't want to read the whole sorry story, the part/CB we are looking for is in bold. thanks :) )

What a week we have had. First, the electric shower went *BANG* with a spark and puff of black smoke while I was it it. We got the electrician in to have a look and check some of the wiring to make sure nothing was amiss and he discovered dangerous wiring with the old hot water tank which had 1 immersion but was running Economy 7 and should have had 2. he recommended we have the tank changed to a double immersion and have it wired in properly which we did. (£500 total - cheap for the peace of mind that the house isn't going to burn down or my family and unborn baby put at risk!!)

The sparky suggested that to save money DH fitted shower himself (Which he is legally allowed to do and perfectly capable) so he did but it keeps tripping the breaker. Sparky came back and has said that the load is probably just too close to the bearing limit on the 30a circuit breaker as we have a very old fuse box (20 years old - original one) and electric showers didn't exist back then. He has suggested either:

1. sending off a spur and running the wiring for the shower through a new style CB which they appear to have done sucessfully with the electric heater in the bathroom. (moderately expensive)

2. replacing the whole fuse box which he has advised us against due to the cost of it and the fact that we might be having the kitchen redone in the next few years and the wall it is on would have to be moved then anyway

3. sourcing a replacement Circuit breaker. The code is BS3781 and we need a 32a, 35a or 40a whichever they actually make! The brand is crabtree.

We have decided to try and do number 3 but are having no success so any ideas where we might get one please?

Sorry for the Essay, I just thought a bit of background info might be useful incase anyone had any other thoughts.

Thanks in advance
Good Enough Club member number 27(2) AND I got me a stalkee!
Closet debt free wannabe -[STRIKE] Last personal loan payment - July 2010[/STRIKE]:T, credit card balance about £3000 (and dropping FAST), [STRIKE]Last car payment September 2010 (August 2010 aparently!!)[/STRIKE]
And a mortgage in a pear tree :D

Comments

  • Morty_007 wrote:
    The sparky suggested that to save money DH fitted shower himself (Which he is legally allowed to do and perfectly capable) so he did but it keeps tripping the breaker. Sparky came back and has said that the load is probably just too close to the bearing limit on the 30a circuit breaker as we have a very old fuse box (20 years old - original one) and electric showers didn't exist back then. He has suggested either:

    1. sending off a spur and running the wiring for the shower through a new style CB which they appear to have done sucessfully with the electric heater in the bathroom. (moderately expensive)

    2. replacing the whole fuse box which he has advised us against due to the cost of it and the fact that we might be having the kitchen redone in the next few years and the wall it is on would have to be moved then anyway

    3. sourcing a replacement Circuit breaker. The code is BS3781 and we need a 32a, 35a or 40a whichever they actually make! The brand is crabtree.

    We have decided to try and do number 3 but are having no success so any ideas where we might get one please?

    Sorry for the Essay, I just thought a bit of background info might be useful incase anyone had any other thoughts.

    Thanks in advance
    The 'code' is the British Standards number,...ie BS3871 and applies to most mcb.s.
    Crabtree make,or made several types of mcb over the years,..C50,Starbreaker,Polestar,etc.The name,or series of the mcb is probably printed on the lid of the distribution board.They come as 30,32 or 40a.
    Your best bet would be to try a local electrical wholesaler like Newey and Eyre,Edmondsons,Senate or C.E.F.
    To comply with Electrical Regulations you need to fit an RCD circuit breaker.If your existing board has no provision for the RCD,you can either replace the whole board,(might be worth doing if a new kitchen is immenent) or just fit a separate enclosure to house the RCD.
  • rygon
    rygon Posts: 748 Forumite
    The BS number you have given is just the british standard for circuit breakers. I dont think thats going to be of any use for finding a cb which you need. The best bet is to find out what type it is. Try taking one of them to b&q and see if they have any that match
    Smile and be happy, things can usually get worse!
  • Morty_007
    Morty_007 Posts: 1,496 Forumite
    Keefy_B wrote:
    The 'code' is the British Standards number,...ie BS3871 and applies to most mcb.s.
    Crabtree make,or made several types of mcb over the years,..C50,Starbreaker,Polestar,etc.The name,or series of the mcb is probably printed on the lid of the distribution board.They come as 30,32 or 40a.
    Your best bet would be to try a local electrical wholesaler like Newey and Eyre,Edmondsons,Senate or C.E.F.
    To comply with Electrical Regulations you need to fit an RCD circuit breaker.If your existing board has no provision for the RCD,you can either replace the whole board,(might be worth doing if a new kitchen is immenent) or just fit a separate enclosure to house the RCD.

    Excellent, thanks.
    I discovered the BS was just british standards number once I had a look around. Have found the right one in a 50amp on ebay but it's too high. Your comment about fitting and RCD interested me. The sparky is coming back to fit an RCD later in the week...will this negate the need to replace the 30amp CB??

    Thanks
    Good Enough Club member number 27(2) AND I got me a stalkee!
    Closet debt free wannabe -[STRIKE] Last personal loan payment - July 2010[/STRIKE]:T, credit card balance about £3000 (and dropping FAST), [STRIKE]Last car payment September 2010 (August 2010 aparently!!)[/STRIKE]
    And a mortgage in a pear tree :D
  • Morty_007 wrote:
    The sparky is coming back to fit an RCD later in the week...will this negate the need to replace the 30amp CB??
    If the RCD wont fit into your distribution board,you may need the 30a mcb to supply the RCD and enclosure.(If that makes sence!)
  • Morty_007
    Morty_007 Posts: 1,496 Forumite
    wonderful, i'll ask him about it. thanks again
    Good Enough Club member number 27(2) AND I got me a stalkee!
    Closet debt free wannabe -[STRIKE] Last personal loan payment - July 2010[/STRIKE]:T, credit card balance about £3000 (and dropping FAST), [STRIKE]Last car payment September 2010 (August 2010 aparently!!)[/STRIKE]
    And a mortgage in a pear tree :D
  • Try these people

    http://www.thefusecompany.co.uk

    they are very dear, but usually have stuff.

    If you post a picture this will help as some manufacturers do MCB's that are copies of some brands (so a copy may fit)

    on another note
    about 60% of homes up here with E7 heating have only 1 immersion heater, this isn't perfect but my gran had this situation for over 10 years with no problems. It is most certainly not dangerous to only have 1 immersion heater.

    The draw backs are:
    1. Less water than a larger dual eliment immersion cylinder.
    2. You can't heat the top half of the cylinder during the day.

    It may be better considering replacing the consumer unit now (you could move it now and re-locate the meter and supply cable when you move the wall away. This will also split the cost (part now and part later)
    baldly going on...
This discussion has been closed.
★ ★ ★ Meet your Ambassadors

Categories

  • All Categories
  • 356K Banking & Borrowing
  • 255K Reduce Debt & Boost Income
  • 456.3K Spending & Discounts
  • 248.5K Work, Benefits & Business
  • 606.3K Mortgages, Homes & Bills
  • 179.1K Life & Family
  • 264.1K Travel & Transport
  • 1.6M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards
Quick Search

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.