Mixer Shower

Hi guys...

Just wanted to check.. am having a mixer shower installed.. the plumber says i need to have a pressure reducing valve for my cold as it runs from mains.. however, for this to happen he would need access to the pipes which are behind my newly tiles walls so obviously a problem there.. is it essential i have this valve.. i just had a new combi boiler (worcester 35CDi) put in (not sure if this info is helpful)

thanks in advance

Comments

  • p4u1_2
    p4u1_2 Posts: 73 Forumite
    Not sure why you should need a pressure reducing valve becouse of the cold water feed being direct from the mains, as with a combi boiler the hot water is also fed from the mains via the combi. I suspect it may be due to the combi being unable to heat water at the same flow rate as the mains cold water feed, and therefore reducing the pressure/flow rate. The cold water feed pressure would therefore have to be reduced to a similar level. Can the valve not be installed further back up the pipe run, i.e. further away from the shower.
  • hkt7383
    hkt7383 Posts: 73 Forumite
    hey.. the problem with putting it further back is still the access problem.. tiles will have to come off somewhere.. thats why im trying to work out if it is really essential.. any other suggestions welcome..
  • plumb1_2
    plumb1_2 Posts: 4,671
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    Forumite
    The best option is to fit the PRV on the incoming mains after the stop tap(usualy under the sink).
    This will supply both your feeds(boiler/taps/shower) with equal pressures. set @ approx 3bar, and dont forget to cross bond.
    A thankyou is payment enough .
  • Mikeyorks
    Mikeyorks Posts: 10,380
    Part of the Furniture 10,000 Posts Combo Breaker
    Forumite
    I had the same problem. Cold feed to the mixer was mains (from a bore hole with very variable pressure depending on whether cows being milked etc).

    Tried to get away with it - but it was useless attempting to use the new shower. As the variability threw the thermostat controls completely. Had the choice of a self adjusting PRV or re-plumbing the cold feed from the cold water tank (which I'd just boosted to 100 galls because of the bore feed occasionally reducing to a trickle).

    Opted for the PRV - as we were able to tuck it just into the shower feed and under the bath. Wherever you place it - it's potentially a serviceable item, so needs to be accessible
    If you want to test the depth of the water .........don't use both feet !
This discussion has been closed.
★ ★ ★ Meet your Ambassadors

Categories

  • All Categories
  • 356K Banking & Borrowing
  • 255K Reduce Debt & Boost Income
  • 456.3K Spending & Discounts
  • 248.5K Work, Benefits & Business
  • 606.3K Mortgages, Homes & Bills
  • 179.1K Life & Family
  • 264.1K Travel & Transport
  • 1.6M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards
Quick Search

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.