  • lambo28
    lambo28 Posts: 191 Forumite
    Thanks everyone. But sorry, you've lost me. Ok, i have checked the downstairs radiators and the return pipe (the side with the lock shield-valve) for most of the radators are fairly-hot. But, the flow pipe is freezing cold.

    After, turning all the radiator valves off around the house, i put all the energy into the downstairs radiators, now they are just luke-warm.

    Once again, thanks!!! and have you got any more suggestions?
  • lambo28
    lambo28 Posts: 191 Forumite
    My diverter valve is a 3-way one, i have removed it and checked it out and it is working fine. I have also bleeded the pump via the big screw and only water comes out, no air. I have also turned the thing inside the pump and it moves freely.
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi

    What speed is the pump on? It's on the black plate on the side 1, 2, 3,

    Corgi Guy.
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • plumb1_2
    plumb1_2 Posts: 4,395 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    My educated guess is that you have an Air-lock, best to drain down completley, includeing the down stairs rads.It is important to drain the lower rads otherwise it will trap air at the top of the drops.

    If the water is very dirty/black you have a sludge in the sysytem and need a powerflush.
  • lambo28
    lambo28 Posts: 191 Forumite
    The speed of the pump is on speed 3.
  • plumb1_2
    plumb1_2 Posts: 4,395 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    lambo28 wrote: »
    The speed of the pump is on speed 3.

    Your pump wont push pass a block of air, or sludge.
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi

    If you turn the cylinder stat down until it clicks off ,turn the boiler stat down low (just above minimum) .Run the c/h. Change the pump speed from 1 to 3. Listen to the system on the different speeds.Does the system seem to respond to the different speeds? Do you hear any air gurgling around. ? Turn off the
    upstairs rads and all but one of the downstairs rads.(pump on No3)
    Follow the pipework from the pump. Is there a 15mm pipe that seems to go nowhere (or maybe runs back into the return from the cylinder) with a red handle gate valve on it. If you do this could be a bypass.(a short circuit.)Turn off the gate valve.
    Corgi Guy.

    Or you could post a photo.
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.2K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.3K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.