When our heating is switched on, the circulating pump (Myson CP53) runs for a couple of seconds and then the main power fuse switch trips.

Tried switching off all other fuse switches but the heating circuit. No change.

Tried swapping the fuse switch. No change.

Isolated pump from mains and switched heating on. No trip: boiler ignited and ran as normal.

Unscrewed the pump vent plug. Rotor shaft can be manually rotated. A small amount of water dripped out when turned.

Does this sound like a pump replacement job or something more complex? I really hope this is a DIY job - a new burner for our kitchen range has just eaten our emergency fund!

The pump has gate valves.

All suggestions appreciated.

FD

Comments

  • knightstyle
    knightstyle Posts: 7,178 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    First the "main power fuse" is not a fuse at all but almost certainly a RCD this is a detector that detects a leak of electricity from the power circuit to earth. It will trip if only a miniscule amount of leakage occurs, 30 thousandths of an amp is typical.
    You probably have some damp somewhere in the pump electrics, could be condensation or a leak.
    Try isolating the circuit, remove the cover on the pump electrics and drying with a hairdryer. Do the same with other components, tank thermostat for example.
    Other than that get someone in to make sure the problem is the pump before replacing it yourself.
    ALWAYS ISOLATE THE SUPPLY BEFORE WORKING ON ELECTRICS.
  • I had a similar problem a few weeks back. Having narrowed it down to the pump, I sourced a spare from a local heating supplies merchant, fitted it myself (easy) and was up and running within hours of original problem. The symptons of your problem were the same as mine. Electrian friend mentioned possible breakdown of internal circuitry of pump assembly. good Luck!
  • baldelectrician
    baldelectrician Posts: 2,467 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Had this last week. When I traced the fault to the pump (with my test equipment), I opened terminal cover up and water ran out :D

    Could have saved testing and just opened pump cover, but that's life.
    baldly going on...
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.9K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.9K Work, Benefits & Business
  • 619.7K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.