Making my central heating and water smart with Shelly - need an electrical relay.

Morning all.

Apologies in advance for the technical nature of this post but I have a Y-Plan central heating and water system and I have bought one of these devices to make it smart:

Shelly 2PM Gen4 | Dual Smart Relay with Power Monitoring & Matter | Shelly Europe

There is a slight issue, however, in that the Shelly has two SPST-NO relays in it.

This works perfectly for the central heating side as the heating is either on or off.

On a Y-Plan, however, things are slightly more complicated with the hot water side as I need two separate contacts, as this is needed to control the actuator. Ultimately, I need an additional mechanical SPDT NO relay, 230v 10A relay.

Can anyone advise which one to get?

There are some many variants out there.

«1

Comments

  • grumpy_codger
    grumpy_codger Posts: 1,766
    1,000 Posts First Anniversary Name Dropper Photogenic
    Forumite

    Just curious…

    What other device will control 'Shelly' making your system 'smart'? And how will this be better than a normal smart CH+HW thermostat?

  • tacpot12
    tacpot12 Posts: 9,592
    Tenth Anniversary 1,000 Posts Name Dropper
    Forumite

    It would be easer to advise you if you can post a wiring diagram of what you are trying to acheive. If you start with the system diagram from here it will be easier to see what you want: Y Plan central heating system

    The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.
  • elsmandino
    elsmandino Posts: 332
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Forumite

    Morning grumpy - I have a server running Home Assistant, which automates everything in my home. There is an integration for Shelly relays, so Home Assistant should give me so much more flexibility than I currently have - e.g. the ability to automatically turn off the heating when nobody is home, boost hot water timer by more than an hour etc.

    Morning tactpot (great names on this forum) -

    This is exactly what I have. The programmer bit is the area I want to replace with a Shelly relay. Connections 2 and 4 are the central heating side and are easy to deal with as Connection 2 is not connected to anything. I can therefore just connect Connection 4 when I need the heating on.

    However, Connections 1 and 3 (for the hot water) are slightly more problematic as it involves a connection that flips from 1 to 3 when power is introduced. The Shelly does not have this built in, so I need a separate relay that flips between these two connections but does so when the Shelly sends a signal to do so.

    Hope that makes sense - it seems Y-Plan heating systems are very clever but quite difficult to get your head around, electrically.

  • Heedtheadvice
    Heedtheadvice Posts: 3,126
    Part of the Furniture 1,000 Posts Name Dropper
    Forumite

    I agree with tacpot. It is unclear to me why you need 3 switched lives so a diagram of the required connections for the Y valve actuator would useful.

    Typically the connections on a 3 port valve are:

    • Blue: Neutral
    • White: Heating/Hot water mid-position or heating off/on control (Live in 1)
    • Grey: Hot water off signal from cylinder thermostat (Live in 2)
    • Orange: Switched Live output back to fire up the boiler and pump [1, 2]Soo

    So two switched Live inputs to valve which you already have from your Shelly .... or am I missing something?

  • elsmandino
    elsmandino Posts: 332
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Forumite

    Hi there.

    The issue is that the Shelly on has the ability to connect one input with one output per channel. If there is no signal, no connections are made. With the hot water side (i.e. connections 1 and 3), either connection 1 or connection 3 must be connected for the system to work - i.e. it will not work if neither are connected. Ultimately, therefore, I need an additional relay that flips between these two connections and controlled by the Shelly itself.

  • grumpy_codger
    grumpy_codger Posts: 1,766
    1,000 Posts First Anniversary Name Dropper Photogenic
    Forumite
    edited 6 August at 11:51AM

    Home Assistant should give me so much more flexibility than I currently have - e.g. the ability to automatically turn off the heating when nobody is home, boost hot water timer by more than an hour etc.

    My smart thermostat (with an app) does all this. Plus geofencing. Honeywell Lyric T6R-HW. I'm sure other thermostats can do the same, but when I checked few years ago mine was the only one with free geofencing.

  • QrizB
    QrizB Posts: 25,151
    10,000 Posts Fifth Anniversary Photogenic Name Dropper
    Forumite

    I need an additional mechanical SPDT NO relay

    I don't think there's any such thing? A SPDT relay has both NO and NC terminals.

    SPDT.jpg

    As for choosing a relay, a lot will depend on the form factor you're looking for.

    If you're putting this all in a DIN enclosure, for example, you might want use something like this:

    https://uk.rs-online.com/web/p/power-relays/1916071

    But if you're hoping to hide it inside a wiring box, you might prefer something else.

    N. Hampshire, he/him. Octopus Intelligent Go elec / Fuse gas / Vodafone BB / iD mobile. Kirk Hill Co-op member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 37 MWh generated, long-term average 2.6 Os.
    Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Ecoflow Stream, Best kettle :-)
  • Section62
    Section62 Posts: 11,817
    10,000 Posts Fifth Anniversary Name Dropper
    Forumite

    On a Y-Plan system you need a controller with an additional output for "HW off". The grey/HW-Off wire of the mid-position valve needs to be energised in order for the valve to move to the CH-only position.

    This is because the hot water off situation can occur either because hot water isn't wanted (the programmer for HW is 'off') or because the cylinder is heated to temperature and the cylinder stat has gone to 'SAT'.

    In the first case there needs to be an output (live) from the programmer to take the mid-position valve to the HW-only position. The lack of voltage on the programmer 'HW On' terminal won't achieve this.

    Hence the need for the programmer/contoller to have three outputs.

  • FreeBear
    FreeBear Posts: 18,904
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    Forumite

    You don't need any double throw relays. Simply have one Shelly to energise the valve, and another to call for heat from the boiler (or a single Shelly 2PM or a Sonoff Dual). Leave Home Assistant to work out which relays to enable, and what order.

    *) I've been using HA to control the heating for quite a few years now, both an antiquated Baxi back boiler, and now a Viessmann combi via OpenTherm. Also have a bunch of sensors dotted around the house to record temperature to help with fine tuning the heating schedual.

    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • elsmandino
    elsmandino Posts: 332
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Forumite

    Thanks for this. You are completely right - a SPDT must have both NO and NC terminal, anyway.

    That suggestion looks exactly what I am after. I might have to do some measuring and, as you say, consider something smaller to try and fit it inside a junction. The specs, however, are perfect.

    Freebear - I think you might have a slightly different set up to me. The Y-plan system is pretty old and, I am told, not used anymore.

★ ★ ★ Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.8K Banking & Borrowing
  • 254.9K Reduce Debt & Boost Income
  • 456.2K Spending & Discounts
  • 248.3K Work, Benefits & Business
  • 605.9K Mortgages, Homes & Bills
  • 179K Life & Family
  • 263.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.