Central Heating Pipes under screed

Hello,

25mm flexible plastic conduit, inside lies 15mm JG SPEEDFIT barrier pipe,no fittings used under screed. The pipe as a 90deg bend,can you for see any problems/Issues.

Many thanks

Comments

  • FreeBear
    FreeBear Posts: 18,907
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    Forumite

    Plastic pipe running under concrete - No issues at all. Standard practice if you are installing underfloor heating.

    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • Boohoo
    Boohoo Posts: 2,530
    Part of the Furniture 1,000 Posts Name Dropper
    Forumite

    Why do you need 2 pipes?

    I don't know about using 2 pipes but wouldn't 1 pipe be enough as it can be used under screed.

  • tacpot12
    tacpot12 Posts: 9,593
    Tenth Anniversary 1,000 Posts Name Dropper
    Forumite

    One larger conduit containing the flow and return pipes would also be fine, but its much easier to install one pipe per one conduit. No problem with it. It's standard/best practice as per FreeBear's comment.

    The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.
  • grumpy_codger
    grumpy_codger Posts: 1,772
    1,000 Posts First Anniversary Name Dropper Photogenic
    Forumite
    edited 9 August at 8:13AM

    It's standard/best practice as per FreeBear's comment

    He referred to underfloor heating practice that doesn't need any extra conduits - just a plastic pipe inside the screed. Generally, there's nothing wrong with using the same practice for a plastic pipe supplying normal radiators.

  • peabottle
    peabottle Posts: 43
    Part of the Furniture 10 Posts Combo Breaker
    Forumite

    Good morning,

    Big thank you for all your input.

  • WIAWSNB
    WIAWSNB Posts: 3,814
    1,000 Posts First Anniversary Name Dropper
    Forumite
    edited 9 August at 3:56PM

    Although plastic pipe is nicely insulated compared to copper, it would still benefit from an additional insulation layer. This would also remove all pressure and potential movement from it. So an alternative method would be to wrap it in insulation before screening over.

    Where is this screed layer - above or below the floor insulation layer? If below, then I'd definitely insulation-sleeve it.

    But your own idea is more than fine in terms of protection. And if it's above the floor insulation layer, then any heat loss should end up in the room!

  • peabottle
    peabottle Posts: 43
    Part of the Furniture 10 Posts Combo Breaker
    Forumite

    Thank you for your reply, the 100mm insulation will be underneath the screed therefore okay, it’s a good point you make though.

★ ★ ★ Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.8K Banking & Borrowing
  • 254.9K Reduce Debt & Boost Income
  • 456.2K Spending & Discounts
  • 248.3K Work, Benefits & Business
  • 605.9K Mortgages, Homes & Bills
  • 179K Life & Family
  • 263.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.