New Rad. Lock Shield pipe cold TRV Hot
steve1500
Posts: 1,465 Forumite
So fitted new Rad in Summer ( done plenty around the house)
As it says TRV pipe nice and hot, but lock shield pipe cold. Turned wide open but still nothing. so a Rad that is only partially warm
Doesn't need bleeding and done balancing. All others rads fine
Any suggestions
TIA
As it says TRV pipe nice and hot, but lock shield pipe cold. Turned wide open but still nothing. so a Rad that is only partially warm
Doesn't need bleeding and done balancing. All others rads fine
Any suggestions
TIA
Private Parking Tickets - Make sure you put your Subject Access Request in after 25th May 2018 - It's free & ask for everything, don't forget the DVLA 
0
Comments
-
Does the lock shield actually open and close? Close both, then disconnect the lock shield from the radiator. Let the radiator drain, then slowly open the lock shield.2006 LBM £28,000+ in debt.
2021 mortgage and debt free, working part time and living the dream1 -
Close down all the other radiators and see if it gets hot.2
-
Thanks - was my thought about the lockshield - is it working. But will try closing all the other Rads off firstPrivate Parking Tickets - Make sure you put your Subject Access Request in after 25th May 2018 - It's free & ask for everything, don't forget the DVLA
2 -
Double-check the lockshield valve, the spindle can sometimes shear or not actually open even though it turns.Try cracking the union on the lockshield side slightly (with a towel ready) to see if water comes through; if not, there’s a blockage or no flow from the return pipe.0
-
My gut says faulty lockshield. ThanksPrivate Parking Tickets - Make sure you put your Subject Access Request in after 25th May 2018 - It's free & ask for everything, don't forget the DVLA
0 -
It could be an air lock in the pipework. Try turn off all the other radiators an domestic hot water. On the radiator that does not work - open the lock shield fully and also the TRV. The full force of the pump pressure will be applied to the pipework and radiator. If there is an airlock it should be forced out.0
-
Try and take and the head off the TRV. When they fail, the fail closed.0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.3K Banking & Borrowing
- 253.7K Reduce Debt & Boost Income
- 454.3K Spending & Discounts
- 245.3K Work, Benefits & Business
- 601.1K Mortgages, Homes & Bills
- 177.6K Life & Family
- 259.2K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards