Fitting Battery to Solar

Options
13

Comments

  • Qyburn
    Qyburn Posts: 3,580 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    tamste said:
    So with 10kWh agreed on export with a 3 phase supply fed through the same hybrid 10 kWh inverter, they are likely not to require an application?

    G98 specifies maximum demand (without load limiting device) as 18 Amps per phase, not 16A.

    Also, the inverter model and capacity is included on the G98, so I presume I would need to make a new application if I changed the inverter?
    Just be clear although you keep writing "kWh" are you actually referring to power, which would be "kW"?

    kWh refers to the quantity of energy, which could mean absolutely any power. For example 10kWh could result from 1kW (power) for 10 hours, 100W for a 100 hours, or 100kW for six minutes. Or any other combination of power and duration giving that product.

    A battery will have both a capacity in kWh and a power rating, possibly different for charge and discharge. For example mine is 9.7kWh, charge and discharge ratings are both 5kW.
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Understood 
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Qyburn said:
    That looks like G.99, in particular the reference to export limit. In which case there should be an Offer in response, which should be accepted before going ahead. Then when the system's commissioned the details of equipment, test results etc are sent to the DNO, and finally (you hope) DNO responds confirming it's all in order and complies with their offer.

    Under G.98 you don't apply, just tell them afterwards.
    Its a G98 as per the declaration
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Update on Inverter - the "compatible" Growatt battery for my MOD 10KTL3-XH inverter is the ARK HV battery system, not the APX which is reserved for the BP model, which I haven't got. Unfortunately cannot find these for sale in the UK, so open to suggestions for compatible alternatives. Looking for 20-30kWh capacity.

  • QrizB
    QrizB Posts: 18,145 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    Ah, your opening post said you had the BP version!
    The ARK HV battery is still a high voltage one (600V - 950V, per the datasheet)
    ... so I don't think you'll find a 3rd party compatible battery. Sorry.
    Dare I suggest asking your original installer? Have they got a source for the ARK batteries?
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    edited 25 June at 6:12PM
    Sorry for confusion on inverter type in the first post .. checked since and its definitely not the BP version, but states its  "AFCI Backup" on the label. It has Battery Positive, Negative and Neutral connection ports.

    The Original installer don't have a source for ARK batteries, so it looks like I will need to change the inverter and add batteries, preferably ones that will give me access to the best import and export rates.

    Looking for suggestions please
  • QrizB
    QrizB Posts: 18,145 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    There aren't that many folk with three-phase so you might not get many first-hand recommendations.
    If you can wait, the three-phase Powerwall is one option (hopefully the "later this year" is a more reliable forecast than all the promises of "full self driving" for their cars).
    Otherwise, I gave an example of a Sunsynk inverter and Fogstar battery back on Page 1:
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    edited 25 June at 8:52PM
    Thanks for the great advice and suggestions QrizB.

    New to this so please bare with me ...

    Why a 8kwh hybrid inverter when the current system is 10kwh, and the solar is 11.4 kwh?

    Current export limit is 10kwh, but suspect this could be increased to 11kWh as it's a 3 phase supply?

    Like the price and capacity of the Fogstar ... Concerned about how I move this to my garage over a gravel driveway... Will find a solution though
  • QrizB
    QrizB Posts: 18,145 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    I may have misread one of your previous posts, but you were talking of having your panels split over two roofs, one facing SE and another facing SW?
    If this is how they were installed, I wouldn't have expected you to ever see the full rated output from the system. Youll get sun.on half of them early in the morning, and half in the evening, but at noon you'll only get 70% out of each set. Which is about 8kW.
    Of course I might have misunderstood, and/or they might not have been installed like that.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • tamste
    tamste Posts: 140 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    edited 26 June at 4:43PM
    In the end, 26 panels were put on the SW roof ... Currently generating ~ 65-70 kWh daily (peak was 80), and shaving at 10kw for ~4-6 hrs a day on the best days. No panels on SE roof.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.