  • doodling
    doodling Posts: 1,271 Forumite
    1,000 Posts Fourth Anniversary Name Dropper
    Hi,

    As others have said, there is no general obligation for the DNO to provide an earth so expecting them to do so is doomed to failure.

    What I suggest you do is get your electrician to explain (and write down clearly) (a) why the DNOs equipment is substandard and (b) what they think needs doing to it.

    Until they have done that then we can only speculate.  If you do want us to speculate then we would need a photo of your incoming supply and all the cabling between that and your consumer unit, via the meter.
  • tetrarch
    tetrarch Posts: 323 Forumite
    Part of the Furniture 100 Posts Name Dropper
    This all sounds very familiar....

    https://forums.moneysavingexpert.com/discussion/6549802/supplier-vs-dno-for-maisonette?

    A similar situation with a horrible back-and-forth. The only saving grace was that the polarity reversal actually constituted a danger and my daughter played Octupus beautifully to force UKPN to attend and sort the problem. 

    Is there a possibility that the boiler could have it's own dedicated earth installed to circumvent the problem?

    Regards

    Tet
  • FreeBear
    FreeBear Posts: 18,193 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    tetrarch said:
    This all sounds very familiar....

    https://forums.moneysavingexpert.com/discussion/6549802/supplier-vs-dno-for-maisonette?

    A similar situation with a horrible back-and-forth. The only saving grace was that the polarity reversal actually constituted a danger and my daughter played Octupus beautifully to force UKPN to attend and sort the problem.
    That thread was never updated with a conclusion - Did UKPN leave the downstairs flat disconnected or did they come back and fix the problem ?

    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • JohnSwift10
    JohnSwift10 Posts: 496 Forumite
    Fourth Anniversary 100 Posts Photogenic Name Dropper
    Go to the media or Resolver?
  • Ectophile
    Ectophile Posts: 7,972 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    My guess is that UKPN aren't refusing to fix it, as such.  They are denying that there is any problem that they are responsible for fixing.

    If the installation is TT, then the customer is responsible for providing an earth rod, and the customer should install an up-front RCD to make sure everything is safe.  Neither is the responsibility of UKPN.

    The DNO decides what sort of installation it is: TT, TN-S or TN-C-S.  They may agree to change it.  But they are under no obligation to do so.  Bodging it by putting a clamp on the incoming supply cable may be unsafe if the outer sheath of that cable isn't properly earthed.

    If the installation is unsafe, then they are allowed to pull the fuse and refuse to reconnect until the customer brings their installation up to standards.   But it's very rare that they do that.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
  • Phones4Chris
    Phones4Chris Posts: 1,240 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    It seems to me some clarification is needed here.
    1) You need to get the DNO - UKPN to formally state what type of supply it is to the property - is it TT, TN-S or TN-C-S ? (TN-S can only be provisioned if the current i/c supply cable is capable of providing that).
    2) Once you know that, your electrician should be able to say exactly what protective equipment including earthing arrangements need to be provisioned for that form of supply if they aren't already present.
    3) What exactly are these "exposed conductive parts" ? 
    (It occurs to me that the supply to the flat upstairs may have nothing whatsoever to do with this and not your responsibility). 
    Where is the upstairs flat's meter?
    Photos of the DNO cut-out and connections to your meter and also cables feeding the flat above will be helpful in understanding this, otherwise it's all speculation.
    4) Is your new boiler installed (who supplied it, BG?) and BG just refusing to connect it because they don't like the earthing or lack thereof?
  • wrf12345
    wrf12345 Posts: 874 Forumite
    Sixth Anniversary 500 Posts
    Perhaps make a note of the return address on the envelope and when the next one arrives, cross out your name on the front of the envelope and mark not known, then bung it in the postbox? The energy company may not care but there should be the possibility of suing them for all the stress caused.
  • born_again
    born_again Posts: 20,357 Forumite
    10,000 Posts Fifth Anniversary Name Dropper
    Go to the media or Resolver?
    Resolver is nothing but a 3rd party who pass your complaint on. They do not get involved in any way to help "Resolve" your complaint.
    Life in the slow lane
  • Phones4Chris
    Phones4Chris Posts: 1,240 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    wrf12345 said:
    Perhaps make a note of the return address on the envelope and when the next one arrives, cross out your name on the front of the envelope and mark not known, then bung it in the postbox? The energy company may not care but there should be the possibility of suing them for all the stress caused.
    Wrong thread, probably https://forums.moneysavingexpert.com/discussion/comment/81281799  ??
  • JohnSwift10
    JohnSwift10 Posts: 496 Forumite
    Fourth Anniversary 100 Posts Photogenic Name Dropper
    Go to the media or Resolver?
    Resolver is nothing but a 3rd party who pass your complaint on. They do not get involved in any way to help "Resolve" your complaint.
    It was just a suggestion.
    Resolver got my complaint resolved when I had one.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.