We're aware that some users are experiencing technical issues which the team are working to resolve. See the Community Noticeboard for more info. Thank you for your patience.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!

Cooker socket, can I plug in a 9kw heater

Options
2»

Comments

  • danrv
    danrv Posts: 1,598 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    edited 23 April 2024 at 11:26PM
    Risteard said:
    danrv said:
    tacpot12 said:
    It's likely that an electrician will be able to change the Cooker Control Unit for a 45A Switch Isolator to allow you to connect a 9kW heater using the existing cable. They will check that the cable is large enough and that the correct circuit breaker has been installed to protect the cable. 
    how many times is 10mm cable or larger used in domestic properties?
    Just for electric showers these days. I still have the 60 amp circuit and 10mm cable for my old 10kW warm air heater. 
    Dedicated circuit certainly needed.

    SOME electric showers. Not all will have such a large cable installed. 
    Yes. 9.5kW would need 10mm, probably 8.5kW too although I run this size on 6mm.
  • Risteard
    Risteard Posts: 2,000 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    danrv said:
    Risteard said:
    danrv said:
    tacpot12 said:
    It's likely that an electrician will be able to change the Cooker Control Unit for a 45A Switch Isolator to allow you to connect a 9kW heater using the existing cable. They will check that the cable is large enough and that the correct circuit breaker has been installed to protect the cable. 
    how many times is 10mm cable or larger used in domestic properties?
    Just for electric showers these days. I still have the 60 amp circuit and 10mm cable for my old 10kW warm air heater. 
    Dedicated circuit certainly needed.

    SOME electric showers. Not all will have such a large cable installed. 
    Yes. 9.5kW would need 10mm, probably 8.5kW too although I run this size on 6mm.

    8.5kW will in almost all usual circumstances be fine on 6mm^2. In fact my 8.5kW shower is installed on an existing 6mm^2 cable.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.