Cooker socket, can I plug in a 9kw heater
Comments
-
Yes. 9.5kW would need 10mm, probably 8.5kW too although I run this size on 6mm.Risteard said:danrv said:
Just for electric showers these days. I still have the 60 amp circuit and 10mm cable for my old 10kW warm air heater.BarelySentientAI said:
how many times is 10mm cable or larger used in domestic properties?tacpot12 said:It's likely that an electrician will be able to change the Cooker Control Unit for a 45A Switch Isolator to allow you to connect a 9kW heater using the existing cable. They will check that the cable is large enough and that the correct circuit breaker has been installed to protect the cable.
Dedicated circuit certainly needed.
SOME electric showers. Not all will have such a large cable installed.0 -
danrv said:
Yes. 9.5kW would need 10mm, probably 8.5kW too although I run this size on 6mm.Risteard said:danrv said:
Just for electric showers these days. I still have the 60 amp circuit and 10mm cable for my old 10kW warm air heater.BarelySentientAI said:
how many times is 10mm cable or larger used in domestic properties?tacpot12 said:It's likely that an electrician will be able to change the Cooker Control Unit for a 45A Switch Isolator to allow you to connect a 9kW heater using the existing cable. They will check that the cable is large enough and that the correct circuit breaker has been installed to protect the cable.
Dedicated circuit certainly needed.
SOME electric showers. Not all will have such a large cable installed.
8.5kW will in almost all usual circumstances be fine on 6mm^2. In fact my 8.5kW shower is installed on an existing 6mm^2 cable.
1
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.9K Banking & Borrowing
- 253.9K Reduce Debt & Boost Income
- 454.7K Spending & Discounts
- 246K Work, Benefits & Business
- 602.1K Mortgages, Homes & Bills
- 177.8K Life & Family
- 259.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards