We'd like to remind Forumites to please avoid political debate on the Forum... Read More »
Should I install an RCD when replacing multi socket in garage?

mark_cycling00
Posts: 752 Forumite

Currently an electricity cable enters the garage from the ground, hits a heavy duty looking fuse and switch, then two wires exit from here
One wire supplies two exterior lights.
The other wire goes to a single socket that is used for a freezer.
I'd really like to change to a multi socket so I can use a power tool occasionally and still have the freezer on.
Power tools are a bit risky so I wondered if I should install something like a 13a RCD at 13a before the multi socket.
The current setup for the whole house passed an electrical inspection about 5 years ago.
Many thanks if you can advise
One wire supplies two exterior lights.
The other wire goes to a single socket that is used for a freezer.
I'd really like to change to a multi socket so I can use a power tool occasionally and still have the freezer on.
Power tools are a bit risky so I wondered if I should install something like a 13a RCD at 13a before the multi socket.
The current setup for the whole house passed an electrical inspection about 5 years ago.
Many thanks if you can advise
0
Comments
-
Not an electrician, but with power tools outside, I always like to add an rcd. You can get plug in ones quite cheaply or one built into a double socket - eg Screwfix item 3133J1
-
Does it run back to your house internal consumer unit and is that rcd protected?0
-
Jonboy_1984 said:Does it run back to your house internal consumer unit and is that rcd protected?
.on the consumer unit (the modern type with flip switches) there is a "garage" labelled fuse.
I was thinking that it might be worth protecting the freezer and rather than the whole circuit cutting out0 -
mark_cycling00 said:Jonboy_1984 said:Does it run back to your house internal consumer unit and is that rcd protected?
.on the consumer unit (the modern type with flip switches) there is a "garage" labelled fuse.
I was thinking that it might be worth protecting the freezer and rather than the whole circuit cutting out1 -
All sockets that could be used with an extension lead outside should be RCD protected - Hopefully you are using metal clad sockets in the garage, in which case, use one like this - https://www.screwfix.com/p/british-general-13a-2-gang-sp-switched-metal-clad-passive-rcd-socket-with-white-inserts/4714p
Her courage will change the world.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
That's a great answer. I haven't purchased anything yet so will get those.
Thanks0 -
FreeBear said:All sockets that could be used with an extension lead outside should be RCD protected - Hopefully you are using metal clad sockets in the garage, in which case, use one like this - https://www.screwfix.com/p/british-general-13a-2-gang-sp-switched-metal-clad-passive-rcd-socket-with-white-inserts/4714p
All socket-outlets everywhere should be RCD protected.
{Signature removed by Forum Team - if you are not sure why we have removed your signature please contact the Forum Team}1 -
FreeBear said:
Hopefully you are using metal clad sockets in the garage,
There's rarely a need to in most domestic garages.
Only IF the sockets could be subject to impact damage in a 'workshop' style use would they become advisable.
All the sockets, switches and heating wiring stuff in my attached garage are plastic... even the Consumer unit and that's from new when built.1 -
mark_cycling00 said:Jonboy_1984 said:Does it run back to your house internal consumer unit and is that rcd protected?
.on the consumer unit (the modern type with flip switches) there is a "garage" labelled fuse.
I was thinking that it might be worth protecting the freezer and rather than the whole circuit cutting out1 -
Thanks for the replies it's a great learning experience.
If sounds like I could check to see if my consumer unit has RCBOs target than just fuses. If they are RCBOs then the circuit might be "safe"
The scenario I'm not sure about yet is as follows: if something dangerous happens to a power tool eg drill through a live wire. Will the entire garage circuit be affected? I'm just concerned about keeping the freezer working in this scenario
Will a metal socket with built in RCD help at all?
Thanks0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350K Banking & Borrowing
- 252.7K Reduce Debt & Boost Income
- 453.1K Spending & Discounts
- 243K Work, Benefits & Business
- 619.9K Mortgages, Homes & Bills
- 176.5K Life & Family
- 255.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- Read-Only Boards
- 15.1K Coronavirus Support Boards