    A thought, I wonder how much water leaking from a cracked exchanger will simply be turned into steam and shoved out the flue?! I'd always assumed that it would end up in the condensate, but a boiler turned up high so only partially condensing is as likely to evaporate the leak, and dispose of it out t'flue.
    So, good call checking the flue gas too - that had not occured to me :neutral:
  • More exciting!
    A thought, I wonder how much water leaking from a cracked exchanger will simply be turned into steam and shoved out the flue?! I'd always assumed that it would end up in the condensate, but a boiler turned up high so only partially condensing is as likely to evaporate the leak, and dispose of it out t'flue.
    So, good call checking the flue gas too - that had not occured to me :neutral:
    Hold on to your seat, it just got more exciting!!

    Right, so I put the green food dye (120ml A LOT i know) into a radiator like 30 mins ago. Kept CH off (it hasnt been on since 16:30). I wasn’t expecting the dye to disperse that quickly.

    in any case, after the dye was put in, I started using some hot water to get things going (left boiler unisolated). I then checked condensate trap and I noticed the slightest shade of discoloured water, but inconclusive, it could be the dirt that accumulates from combustion etc right?

    So I take trap off, wipe a bit with some tissue around the outlet, and I’m almost certain of a tint of green.

    With the HX hot due to useage of water, I isolated, then noticed that the pressure is rapidly decaying close to zero, takes about 5 mins from 1 bar to near zero.

    I’ll keep using hot water for a few hours to keep the HX hot and the crack open, il write back here my findings and how that water colour develops. Il need to keep allowing CH water into the boiler by deisolating every 5 mins to keep the green dye entering

    If it turns out to be the HX, despite me needing to fork out a huge amount, it’ll give me huge piece of mind. Il also be swapping out all old rads and putting stainless steel in all wet rooms. New valves on EVERY rad too. We aren’t taking any prisoners.
  • Also an issue I’m facing, boiler isolated at 0.4 bar, and even when only using DHW was rising fast towards 2.5 bar+ so I quickly deisolated. Seems like I’m unable to do that test.

    not that it should matter with the dye in the system, given I can see green in the condensate anyway. If anything keeping it deisolated will allow the dye into the boiler and prove the result
  • cheme7676
    cheme7676 Posts: 129 Forumite
    Sixth Anniversary 100 Posts Name Dropper Combo Breaker
    Final update: Viessmann Vitodens 050 35kW ordered. Also brand new radiators with new valves ordered for entire house. Gas safe engineer expected to come within the next couple of weeks to install everything. Thanks all for your help
  • ThisIsWeird
    ThisIsWeird Posts: 7,935 Forumite
    1,000 Posts Second Anniversary Name Dropper
    Phew!
    It does all suggest a failed MainX.
    The isolated boiler shooting up in pressure suggests a non-functioning EV - that shouldn't happen.
    And the very obvious drop in pressure from 1 bar to zero on the isolated boiler might just be due to the boiler cooling and the small amount of stored water inside contracting, espec with the faulty EV, but it's sooo dramatic a fall, that it does also imply the MainX.
    Anyhoo, new boiler on the way! Chances are, by far I think, that the boiler was the culprit.
  • Did this work? I also have a c35 ideal boiler, pressure all over the place dropping pressure while heating on, no visable leaks had BG out three times once for just the service ,they recharged ev then pressure dropped over night, then changed ev and pr valve and dropped over 6 days, no visable signs of leak anywhere.  It is doing my head in.  Why such random drops, currently dropping at night. Pressure 2.6 when hot and dropping below 0.5 Cold. 
  • Did this work? I also have a c35 ideal boiler, pressure all over the place dropping pressure while heating on, no visable leaks had BG out three times once for just the service ,they recharged ev then pressure dropped over night, then changed ev and pr valve and dropped over 6 days, no visable signs of leak anywhere.  It is doing my head in.  Why such random drops, currently dropping at night. Pressure 2.6 when hot and dropping below 0.5 Cold. 
    Sorry to hear you're having problems. It did work for me yes.

    It's a bit unconventional, but I put food colouring into my system which told me within minutes that my boilers HX was faulty. Due to the nature of the crack, that was the only way I could find it.

    If you've tried everything, there's no harm in putting some green colouring in and then monitoring the colour of your condensate trap. If the water in there starts turning green, that's your smoking gun that it's time to purchase a new boiler
  • ThisIsWeird
    ThisIsWeird Posts: 7,935 Forumite
    1,000 Posts Second Anniversary Name Dropper
    cheme7676 said:
    Did this work? I also have a c35 ideal boiler, pressure all over the place dropping pressure while heating on, no visable leaks had BG out three times once for just the service ,they recharged ev then pressure dropped over night, then changed ev and pr valve and dropped over 6 days, no visable signs of leak anywhere.  It is doing my head in.  Why such random drops, currently dropping at night. Pressure 2.6 when hot and dropping below 0.5 Cold. 
    Sorry to hear you're having problems. It did work for me yes.

    It's a bit unconventional, but I put food colouring into my system which told me within minutes that my boilers HX was faulty. Due to the nature of the crack, that was the only way I could find it.

    If you've tried everything, there's no harm in putting some green colouring in and then monitoring the colour of your condensate trap. If the water in there starts turning green, that's your smoking gun that it's time to purchase a new boiler
    Nice. I've heard of that as a suggestion, but never with an actual result!
    Also heard of adding perfume, and sniffing everywhere.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243K Work, Benefits & Business
  • 597.4K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 256K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.