Has anyone had a combi conversion with microbore?

Options
2»

Comments

  • kittennose
    kittennose Posts: 145 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Vortigern said:
    Looking at converting our system to a combi, but stressed about costly leaks given our pipework is 8mm microbore and 30+ years old.

    Has anyone had this done successfully?

    Yes, original 1988 system changed from open vent cylinder with feed & expansion, to combi.  No issues with leakage.

    How much of your pipework is microbore? Mine was 22mm flow & return from boiler to cylinder, then 15mm distribution and finally a short length of coiled 8mm to each radiators. You don't see the 15mm pipe until you take some floorboards up.
    Not sure, ours goes into the actual walls
  • kittennose
    kittennose Posts: 145 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Maybe I should take some floorboards up - our 8mm pipes all go into the walls though, not the floor. That's why leaks stress me out.
  • ThisIsWeird
    ThisIsWeird Posts: 7,935 Forumite
    1,000 Posts Second Anniversary Name Dropper
    What will lifting floorboards achieve? Unless you leave them up for a few weeks after the conversion.
    If you are really concerned, to the point of you not being able to relax after the work, then insist on a pressure test as FreeBear suggested. Your new system should not get above 3bar at any time, even during faults - the boiler will have a safety release valve set at that -  so a, say, 5 bar test should give you complete peace of mind. 
  • FreeBear
    FreeBear Posts: 18,257 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    ThisIsWeird said: If you are really concerned, to the point of you not being able to relax after the work, then insist on a pressure test as FreeBear suggested. Your new system should not get above 3bar at any time, even during faults - the boiler will have a safety release valve set at that -  so a, say, 5 bar test should give you complete peace of mind. 
    BS EN 14276 is (I believe) the standard that covers plumbing & heating systems - One normally conducts a pressure test at between 1.5 & 2 times the maximum working pressure of the system. So if the boiler safety valve lifts at 3 bar, the test on the rest of the system should be at 4.5-6 bar.
    Radiators, pipes, and fittings are generally certified for a maximum of 10 bar, so a 5 bar test pressure is generally accepted as reasonable. Any plumber familiar with installing underfloor heating should be equipped to do pressure tests on a heating.

    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.