Worcester boiler central heating temp

My Worcester Greenstar Junior boiler has a dial for the central heating temp going from 0 to 7. The heating temp range is 40 to 82 degrees according to the instructions. If I want a temp of about 60 degrees would that be 3.5 on the dial or is it not that simple? Any help appreciated!
«13

Comments

  • JSHarris
    JSHarris Posts: 374 Forumite
    100 Posts Name Dropper
    Best bet would be to try and measure the radiator temperature.  Simplest way to do that is with an IR thermometer.  These are pretty cheap and I've found one to be extremely useful.  I have one that cost about a tenner and is still going strong after several years.  Just point it at a radiator or close to the flow pipe from the boiler and adjust the control to see what temperature you get.
  • JSHarris said:
    Best bet would be to try and measure the radiator temperature.  Simplest way to do that is with an IR thermometer.  These are pretty cheap and I've found one to be extremely useful.  I have one that cost about a tenner and is still going strong after several years.  Just point it at a radiator or close to the flow pipe from the boiler and adjust the control to see what temperature you get.
    Fantastic tip - thanks. Soon I shall know the temperature of everything in the entire house!
  • JSHarris
    JSHarris Posts: 374 Forumite
    100 Posts Name Dropper
    JSHarris said:
    Best bet would be to try and measure the radiator temperature.  Simplest way to do that is with an IR thermometer.  These are pretty cheap and I've found one to be extremely useful.  I have one that cost about a tenner and is still going strong after several years.  Just point it at a radiator or close to the flow pipe from the boiler and adjust the control to see what temperature you get.
    Fantastic tip - thanks. Soon I shall know the temperature of everything in the entire house!

    Mine sits on the dining room table and regularly gets picked up to measure things.  It got loads of use when the plague was rampant, as a quick check to see if either of us was running a high temperature.  Only thing to watch with them is that they give a crazy reading if pointed at anything shiny, like glass, a mirror or polished metal (like a chrome towel rail) as they are calibrated to give an accurate reading from surfaces that aren't very reflective.
  • lohr500
    lohr500 Posts: 1,362 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Or buy a clip on pipe thermometer which in my experience will be more accurate than an IR hand held thermometer. Brannan are a reputable brand and can be bought for not much more than £10. I have two. One on the flow pipe from the boiler and one on the return. Easy to then check and adjust the flow and return temps.
  • lohr500 said:
    Or buy a clip on pipe thermometer which in my experience will be more accurate than an IR hand held thermometer. Brannan are a reputable brand and can be bought for not much more than £10. I have two. One on the flow pipe from the boiler and one on the return. Easy to then check and adjust the flow and return temps.
    I'll probably get both as the IR thermometer will be useful for other things too. Can also test the accuracy which will be interesting.
  • FreeBear
    FreeBear Posts: 18,297 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    My Worcester Greenstar Junior boiler has a dial for the central heating temp going from 0 to 7. The heating temp range is 40 to 82 degrees according to the instructions. If I want a temp of about 60 degrees would that be 3.5 on the dial or is it not that simple? Any help appreciated!

    Min - 40°C
      1  -  47°C
      2  -  53°C
      3  -  61°C
      4  -  68°C
      5  -  74°C
      6  -  80°C
    Max - 82°C

    So for a 60°C flow temperature, set the dial to 3.
    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • gazb_2
    gazb_2 Posts: 59 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    We have the same boiler. What number would you recommend for a bungalow with 9” solid walls with radiators? Thanks 
  • FreeBear said:
    My Worcester Greenstar Junior boiler has a dial for the central heating temp going from 0 to 7. The heating temp range is 40 to 82 degrees according to the instructions. If I want a temp of about 60 degrees would that be 3.5 on the dial or is it not that simple? Any help appreciated!

    Min - 40°C
      1  -  47°C
      2  -  53°C
      3  -  61°C
      4  -  68°C
      5  -  74°C
      6  -  80°C
    Max - 82°C

    So for a 60°C flow temperature, set the dial to 3.
    Oh wow so it turns out the photocopied manual I was left with is missing this bit of crucial information. Thanks so much for posting the link!
  • QrizB
    QrizB Posts: 18,754 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    gazb_2 said:
    We have the same boiler. What number would you recommend for a bungalow with 9” solid walls with radiators? Thanks 
    As low as is comfortable.
    This will involve choosing a lower number when the weather is warm, and a higher one when it's cold.
    It's a manual method of weather compensation.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • Ectophile
    Ectophile Posts: 8,028 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    gazb_2 said:
    We have the same boiler. What number would you recommend for a bungalow with 9” solid walls with radiators? Thanks 

    As low as you can get away with. Modern boilers are more efficient at lower temperatures.
    But if the house never gets up to temperature, then it's too low.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.5K Banking & Borrowing
  • 253.3K Reduce Debt & Boost Income
  • 453.9K Spending & Discounts
  • 244.5K Work, Benefits & Business
  • 599.8K Mortgages, Homes & Bills
  • 177.2K Life & Family
  • 258.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.