Battery maximum output

My battery, which has a 6.5 kWh capacity (LG RESU6.5), seems to have a maximum output of about 2.67 kW.  I'm not sure if this limit is set by the battery or by the inverter but it's a bit irritating because it means even if the battery is fully charged I cannot boil a 3 kW kettle without importing some electricity.  I don't recall ever seeing this issue discussed here so I don't know if this issue is normal or not.  If it's something that can vary then it should be quite an important consideration when choosing an inverter & battery conversation.  Thoughts?  
Reed
«13

Comments

  • In Givenergy’s case it’s inverter driven- their 1st Gen Hybrid would charge my 9.5kWh battery at 2.6kWh but the Gen 2 or 3 will charge the same battery at 3.6kWh. I found this out just before my install and immediately got the installer to swap the specced Gen 1 for a Gen 2. Some hybrid inverters like Sunsynk boast they will charge batteries at the full capacity of the inverter e.g. at 5kWh for a 5kW inverter. 
    Smart Tech Specialist with Octopus Energy Services (all views my own). 4.44kW SW Facing in-roof array with 3.6kW Givenergy Gen 2 Hybrid inverter and 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L (R290) ASHP. #gasfree since July ‘23
  • QrizB
    QrizB Posts: 16,504 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    I'm on my phone with dodgy 4G coverage, so I can't search effectively - the specs for your battery and inverter should tell you what discharge power each of those are capable of. The only other limits will be the connections from battery to inverter, and inverter to house.
    I would expect there to be a battery discharge current limit in software in your inverter, and a separate charge current limit.

    (For slightly involved reasons, I've limited my homebrew battery to a maximum output of 1250W (25A at 50V-ish). I bought a lower-powered kettle :) )
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • I was thinking more about discharging than charging as it looks to me as if the charging limit may vary according to the state of charge.  And my inverter knows what model of battery I have but seems to be imposing a smaller limiting discharge power than the battery specifications suggest, if I am reading these correctly.   
    Reed
  • Discharge rates are limited to preserve battery life. I can change them for my (Solax) battery but wouldn't want to ask I presume the manufacturer has chosen a fair balance between maximising power and looking after the battery.  I'm also limited to about 2.7kW. If the sun is shining I'm find but otherwise I start to import  - but it's not a great deal.  

    Charging also follows a similar pattern. It starts off at a maximum rate (which I'm never at risk of wanting to exceed) but then reduces as it gets close to maximum. 
    Install 28th Nov 15, 3.3kW, (11x300LG), SolarEdge, SW. W Yorks.
    Install 2: Sept 19, 600W SSE
    Solax 6.3kWh battery
  • ed110220
    ed110220 Posts: 1,534 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    It's not something I thought much about either. My SPH5000 inverter can output 5 kW from the PV but is limited to 3 kW from the batteries. It's a bit irritating importing when you have energy in the batteries, as we often do because we have an induction hob and electric oven. I've learned to not use too many rings at once, bring things to the boil a bit more slowly (medium high rather than full power) etc. But the plus side is that it's more of an irritation and typically we don't go above 3 kW for long, so although you might be drawing a lot of power it doesn't add up to much.
    Solar install June 2022, Bath
    4.8 kW array, Growatt SPH5000 inverter, 1x Seplos Mason 280L V3 battery 15.2 kWh.
    SSW roof. ~22° pitch, BISF house. 12 x 400W Hyundai panels
  • 1961Nick
    1961Nick Posts: 2,101 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    Both the battery & the inverter will have a maximum output so in this case it could be either.

    Pylontech US2000 batteries each have a maximum output of 1.2kWh. So if you want to maximise your Sofar ME3000 or Luxpower inverter you'll need 3 batteries.
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • ispookie666
    ispookie666 Posts: 1,194 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    edited 16 September 2023 at 7:55AM
    They are limited by Inverter usually.  Sometimes, the BMS might have these limits set in.  But often, it will be set at 1C max, which means the battery will be able to supply energy but will empty in 1 hr, which would be 6.5KWh.  But you will unlikely be able to extract this, as the conversion losses and heat built-up will reduce the output efficiency.  

    Yes, choosing the inverter output sizing and response times would be important.  
    “Don't raise your voice, improve your argument." - Desmond Tutu

    System 1 - 14 x 250W SunModule SW + Enphase ME215 microinverters (July 2015)
    System 2 - 9.2 KWp + Enphase IQ7+ and IQ8AC (Feb 22 & Sep 24) + Givenergy AC Coupled inverter + 2 * 8.2KWh Battery (May 2022) + Mitsubishi 7.1 KW and 2* Daikin 2.5 KW A2A Heat Pump
  • Discharge rates are limited to preserve battery life. I can change them for my (Solax) battery but wouldn't want to ask I presume the manufacturer has chosen a fair balance between maximising power and looking after the battery.  I'm also limited to about 2.7kW. If the sun is shining I'm find but otherwise I start to import  - but it's not a great deal.  

    Charging also follows a similar pattern. It starts off at a maximum rate (which I'm never at risk of wanting to exceed) but then reduces as it gets close to maximum. 
    Do you have a single battery setup? My dual battery solax can charge / discharge at 5kw+
  • zeupater
    zeupater Posts: 5,382 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    edited 20 September 2023 at 3:36PM
    My battery, which has a 6.5 kWh capacity (LG RESU6.5), seems to have a maximum output of about 2.67 kW.  I'm not sure if this limit is set by the battery or by the inverter but it's a bit irritating because it means even if the battery is fully charged I cannot boil a 3 kW kettle without importing some electricity.  I don't recall ever seeing this issue discussed here so I don't know if this issue is normal or not.  If it's something that can vary then it should be quite an important consideration when choosing an inverter & battery conversation.  Thoughts?  
    Hi
    First thought ... if it's an issue, buy a ~1kW kettle - it's the cheapest & most easily addressable solution by far!
    HTH - Z

    "We are what we repeatedly do, excellence then is not an act, but a habit. " ...... Aristotle
    B)
  • Qyburn
    Qyburn Posts: 3,409 Forumite
    1,000 Posts Fourth Anniversary Name Dropper
    zeupater said:
    My battery, which has a 6.5 kWh capacity (LG RESU6.5), seems to have a maximum output of about 2.67 kW.  I'm not sure if this limit is set by the battery or by the inverter but it's a bit irritating because it means even if the battery is fully charged I cannot boil a 3 kW kettle without importing some electricity.  I don't recall ever seeing this issue discussed here so I don't know if this issue is normal or not.  If it's something that can vary then it should be quite an important consideration when choosing an inverter & battery conversation.  Thoughts?  
    Hi
    First thought ... if it's an issue, buy a ~1kW kettle - it's the cheapest & most easily addressable solution by far!
    HTH - Z

    There are plenty of 2200W or 2400W kettles available. Having said that, have you measured yours? Our Russell Hobbs is sold as "3000W" but actually draws 2700W.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.7K Work, Benefits & Business
  • 619.5K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.