Sunology Solar Station - will this work?
Comments
-
These small systems with up to 800W (600 in Germany currently) are often marketed as Balcony systems in Europe. They seem very popular at the moment and are available from the likes of Hofer (Aldi) and the local B&Q equivalent here in Austria for about €700. I live in a very small village and know of a number of these systems that have gone up in the last year or so. They are popular because they are allowed without onerous permissions and paperwork, they do cut the supply if there is no grid available and are perfectly safe if installed correctly so should be on a dedicated circuit in UK.Living the dream in the Austrian Alps.0
-
Can you clarify or expand that? The previous post just said it needs RCD protection and some comment about "main electrical panel" which I don't think is a term defined in the regs. To give an example on the latter, where the tails are split to serve more than one DB, which is considered "main"?No it will not comply with UK wiring regs (unless you install a dedicated circuit as described in the previous post).0 -
I can't think of any clause in 7671 that this system itself would be breaking.0
-
Aside from wiring regs is any sort of DNO notification and/or approval needed?0
-
Approval - no, it's under the size requirement.mmmmikey said:Aside from wiring regs is any sort of DNO notification and/or approval needed?
Notification - maybe, I don't think there's precedent and the notification process is designed for permanent installations.1 -
CSI_Yorkshire said:I can't think of any clause in 7671 that this system itself would be breaking.I don't have a copy to hand but according to page 11 of this pdf guide it's Regulation 712.411.3.2.1.1
N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill Coop member.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.0 -
I'll have to look up the wording of that tomorrow in the office - seems like you say it's something to do with not having it's own circuit..QrizB said:CSI_Yorkshire said:I can't think of any clause in 7671 that this system itself would be breaking.I don't have a copy to hand but according to page 11 of this pdf guide it's Regulation 712.411.3.2.1.10 -
Realistically, I just wonder how much a 800kWp array would generate in practical terms? Yes, on a bright summer’s day the output would cover the house baseload with the rest going to the Grid unless some appliance was in use. On a Winter’s day when even my 6.35kWp can produce very little at any given time with daily outputs as low as 300Wh, then this type of array is arguably of very little use.The FAQs say that the system is compatible with Linky smart meters which suggests that export to the Grid is recorded. This should be the same for SMETS2 meters but I wonder how suppliers will treat these devices for SEG purposes?
If I decided that I would benefit from getting this type of solar generator I might look at this as an alternative offering:
https://uk.jackery.com/?gad=10 -
Having now looked it up - there is no part 411 in section 712 any more.QrizB said:CSI_Yorkshire said:I can't think of any clause in 7671 that this system itself would be breaking.I don't have a copy to hand but according to page 11 of this pdf guide it's Regulation 712.411.3.2.1.1
There was in the original 18th edition, and it said:
"On the AC side, the PV supply cable shall be connected to the supply side of the overcurrent protective device for automatic disconnection of circuits supplying current-using equipment"
The entire section on automatic disconnection has been removed by the latest edition.1 -
That makes some sense. If the PV system was on the load side, it could create an overcurrent that does not trip the breaker. So could still be on a separate DB as I described, but not a sub-DB.Having now looked it up - there is no part 411 in section 712 any more.
There was in the original 18th edition, and it said:
"On the AC side, the PV supply cable shall be connected to the supply side of the overcurrent protective device for automatic disconnection of circuits supplying current-using equipment"
The entire section on automatic disconnection has been removed by the latest edition.1
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.2K Banking & Borrowing
- 253.6K Reduce Debt & Boost Income
- 454.3K Spending & Discounts
- 245.3K Work, Benefits & Business
- 601K Mortgages, Homes & Bills
- 177.5K Life & Family
- 259.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards