Faulty generation meter

Options

I passed 30000 kwh last week and have noted on my geo several 10 plus kwh days since then so when I looked at my generation meter just after midday I was surprised to see it say 30007.8, since then we added another 4 kwh this afternoon but just checked and it says 30008.4.

Something is clearly wrong, my panels are generating as they should but the generation meter is creeping up at a fraction of its correct speed any ideas what is wrong and who I contact?

«1

Comments

  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper

    Ask your FIT provider what the proceedure is for a meter swap. It'll probably be photographs of both old & new meters & possibly a copy of the NIC certificate of compliance for the electrical work.

    Any qualified electrician can change your meter & supply the necessary paperwork.

    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • Krakkkers
    Krakkkers Posts: 1,291 Forumite
    1,000 Posts Second Anniversary Name Dropper

    Thanks, who pays for this?

  • Grandad2b
    Grandad2b Posts: 352 Forumite
    Part of the Furniture 100 Posts Photogenic Name Dropper

    Is your installation under warranty?

  • Krakkkers
    Krakkkers Posts: 1,291 Forumite
    1,000 Posts Second Anniversary Name Dropper

    I have had the system 7.5 years now, the inverter has an insurance backed guarantee of 10 years.

    System seems to be behaving so far today, i have generated 0.7 kwh and 0.7kwh has been registered on the generation meter, iboost is sending power to the hot water tank, all good.

    But over the last week or 2 i think there is about 90 kwh that was generated but not on the generation meter.

    Will watch it it today and make sure all generation is added to the generation meter and will also try to get in my attic to have a look at the inverter to see if there are any faults showing.

  • Krakkkers
    Krakkkers Posts: 1,291 Forumite
    1,000 Posts Second Anniversary Name Dropper

    Update… Been in my attic, there are spiders in there so it was an ordeal.

    Inverter says total 30328 kwh (7.5 years) generation meter says 30012.

    Inverter says last month 462 kwh but only 300 added to generation meter?

    Inverter appears to be ok, no alarms and sensible data, i think it has done this before when generation has simply not been recorded on my meter.

    Overall its only a 1% difference between the inverter and the meter but something seems amiss, any ideas why?

  • Alnat1
    Alnat1 Posts: 3,864 Forumite
    1,000 Posts Third Anniversary Photogenic Name Dropper

    My generation meter shows 5337 but inverter data is showing 4983. That's only 14 months after install and a much bigger % difference.

    Barnsley, South Yorkshire
    Solar PV 5.25kWp SW facing (14 x 375) Lux 3.6kw hybrid inverter installed Mar 22 and 9.6kw Pylontech battery 
    Daikin 8kW ASHP installed Jan 25
    Octopus Cosy/Fixed Outgoing 
  • jimjames
    jimjames Posts: 18,678 Forumite
    Part of the Furniture 10,000 Posts Photogenic Name Dropper
    Krakkkers said:

    Inverter says total 30328 kwh (7.5 years) generation meter says 30012.

    Overall its only a 1% difference between the inverter and the meter but something seems amiss, any ideas why?

    It's entirely normal for the inverter and generation meter to read different numbers overall, the meter is calibrated, the inverter isn't. That's not to say your meter isn't faulty but a long term difference of 1% is not a problem. A short term difference of 50% is though! I suspect it will be your responsibility and cost to replace but the longer you wait the more you are losing out by the looks of it. My inverter failed and I was very keen to get a new one asap as any delay was costing money and coming into the summer could really escalate.
    Remember the saying: if it looks too good to be true it almost certainly is.
  • Krakkkers
    Krakkkers Posts: 1,291 Forumite
    1,000 Posts Second Anniversary Name Dropper
    Its the generation meter thats faulty, i was just in the garage and saw the meter display go to all 8s and come back 5 kwh lower.
    At the time 17.7 kwh generated and 12.6 kwh added to the meter.
    Its changing the display.

  • Krakkkers
    Krakkkers Posts: 1,291 Forumite
    1,000 Posts Second Anniversary Name Dropper
    And just saw it jump back another 0.3 kwh
  • legoman62
    legoman62 Posts: 4,984 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 3 May 2023 at 10:04PM
    My SMA inverter reads 1% higher than my gen meter. 
    I periodically lower the inverter reading to keep the numbers the same.
    16 Sanyo Hit 250s.4kWp SMA 3.8kWp inverter. SW roof. 28° pitch. Minimal shade. Nov 2011 install. Hybrid car. Ripple Kirk Hill. N.E Lincs Coast.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244K Work, Benefits & Business
  • 599K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.