BOILER TEMPERATURE

Options
13»

Comments

  • jvjack
    jvjack Posts: 361 Forumite
    Fifth Anniversary 100 Posts Name Dropper
    edited 11 March 2023 at 9:27PM
    vic_sf49  said  "I've been running boiler flow temps since late Dec...a bit haphazardly, " 
    Same here. Haphazardly.   Cant work it out / whats best etc     
    What does 3.5*  5.0* mean . is that your radiator setting 
    Zandoni  above has noticed people say 60 degrees is too low on very cold days and i think so far thats looking true. 
  • Alnat1
    Alnat1 Posts: 3,869 Forumite
    1,000 Posts Third Anniversary Photogenic Name Dropper
        
    What does 3.5*  5.0* mean . is that your radiator setting 

    Some boilers have a dial to set the water temperature but they don't tell you what temperatures they relate to. Some have numbers, mine simply has min, eco and max..
    Barnsley, South Yorkshire
    Solar PV 5.25kWp SW facing (14 x 375) Lux 3.6kw hybrid inverter installed Mar 22 and 9.6kw Pylontech battery 
    Daikin 8kW ASHP installed Jan 25
    Octopus Cosy/Fixed Outgoing 
  • markin
    markin Posts: 3,860 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper Photogenic
    jvjack said:
    vic_sf49  said  "I've been running boiler flow temps since late Dec...a bit haphazardly, " 
    Same here. Haphazardly.   Cant work it out / whats best etc     
    What does 3.5*  5.0* mean . is that your radiator setting 
    Zandoni  above has noticed people say 60 degrees is too low on very cold days and i think so far thats looking true. 
    Bosh greenstar, 3.5 is 64.5 degrees (3 = 61, 4 =68
  • vic_sf49
    vic_sf49 Posts: 688 Forumite
    Part of the Furniture 500 Posts Name Dropper
    markin said:
    jvjack said:
    vic_sf49  said  "I've been running boiler flow temps since late Dec...a bit haphazardly, " 
    Same here. Haphazardly.   Cant work it out / whats best etc     
    What does 3.5*  5.0* mean . is that your radiator setting 
    Zandoni  above has noticed people say 60 degrees is too low on very cold days and i think so far thats looking true. 
    Bosh greenstar, 3.5 is 64.5 degrees (3 = 61, 4 =68

    Yes, the 3.5* or 5.0* are the boiler flow temps / dial on my boiler.

    Thanks @Markin...I couldn't remember my boiler to even look it up. D'oh.
  • Postik said:
    "As the many adverts say - turn your boiler down to 60 degrees and save money."

    Yes, it will, in theory, but what they fail to add is that doing it is not recommended for non combination boilers.

    Why is it not recommended for non combination boilers?  I only ask because I don't have a combi any longer and I recently turned mine down to 60 degrees
    Because if the cylinder set temperature is higher than the boiler flow temperature, the boiler will never switch off, it will just cycle. I run my system boiler at 50C with a cylinder temperature of 55C. With my present tariffs it is cheaper for me to top up the boiler with solar plus grid rather than use gas. 
  • "Some boilers have a dial to set the water temperature but they don't tell you what temperatures they relate to. Some have numbers, mine simply has min, eco and max.. "

    My WB Greenstar 15Ri (conventional condensing) has no flow temp. display nor numbers on the control knob. Only a black "tapered" line from min. to max.
    I do have two clip on rotary thermometers on the flow and return, directly above the boiler, to give some indication.

  • Alnat1
    Alnat1 Posts: 3,869 Forumite
    1,000 Posts Third Anniversary Photogenic Name Dropper
    edited 12 March 2023 at 2:18PM

    I do have two clip on rotary thermometers on the flow and return, directly above the boiler, to give some indication.

    I used a couple of food probes and some black tape, at least it gave me a rough idea of the temperatures.
    Barnsley, South Yorkshire
    Solar PV 5.25kWp SW facing (14 x 375) Lux 3.6kw hybrid inverter installed Mar 22 and 9.6kw Pylontech battery 
    Daikin 8kW ASHP installed Jan 25
    Octopus Cosy/Fixed Outgoing 
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.1K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.