My smart meter IHD has been giving trouble for sometime now and although I have reported it numerous times to my energy provider they clearly have zero interest in replacing it.
As such I bought this from Aliexpress.
https://a.aliexpress.com/_EzwkEQd
Now uptill now I had assumed that my IHD was giving a true reading and that my Myenergi EDDI was over reading however I noticed that this device was in lockstep with the EDDI. As such I used a clamp meter to measure the current on my incoming line multiplied this by the actual house voltage =243v and hey presto it tuns out that it is actually the IHD that is under reading??
The above device is not the prettiest but it is very functional, provides current and historical data for hour, day, week etc and you can input your tariff to get a running view of costs. Which by the way have tallied with my actual costs on my providers page.
As such I bought this from Aliexpress.
https://a.aliexpress.com/_EzwkEQd
Now uptill now I had assumed that my IHD was giving a true reading and that my Myenergi EDDI was over reading however I noticed that this device was in lockstep with the EDDI. As such I used a clamp meter to measure the current on my incoming line multiplied this by the actual house voltage =243v and hey presto it tuns out that it is actually the IHD that is under reading??
The above device is not the prettiest but it is very functional, provides current and historical data for hour, day, week etc and you can input your tariff to get a running view of costs. Which by the way have tallied with my actual costs on my providers page.
15 x JASolar 405w Panels installed 25/11/22, 5 SE, 5S, 5SW
3 x Uhome LFP2400 batteries
Luxpower ACS 3600 Battery Inverter
2 x. Toyota Prius
3 x Uhome LFP2400 batteries
Luxpower ACS 3600 Battery Inverter
2 x. Toyota Prius
0
Latest MSE News and Guides
Replies
That is not the way an electricty meter usually does it. A leccy meter will normally have a shunt in series with the mains supply which measures the actual current rather than the estimated current from the magnetic field and so can measure the current to a much better accuracy than a clamp and take into account the instantaneous variation in voltage - my voltage varies between around 245 to 253 and so will be more accurate than a clamp.
As @zeupater points out the load on the mains is also subject to the vagaries of power factor, stuff with motors like washing machines, dryers, fridges, freezers etc have poor power factor as do LED bulbs (especially cheap ones).
AFAIK domestic meters dont take power factor info consideration(although industrial meters do). However as the waveform gets highly distorted when some of these load are on, then it will affect the accuracy of a current clamp more than it will a shunt.
Although you may be able to compare all the meters, there will be a difference between clamps and shunts which will manifest itself over time and will depend on what stuff is turned on and for how long. I'm also guessing that most of these clamp devices use the same Chinese chips and wont go through the sort of quality checking and testing that leccy meters have to endure.
They may be near enough for what they are intended but not accurate enough for billing purposes.
January figures for import...
Meter: 652kWh
GEO: 649kWh
Myenergi: 648kWh
Jan figures for generation...
Meter: 162kWh
GEO: 161kWh
Myenergi: 160kWh