Radiator drain valve advice please - 10mm pipes

ChasingtheWelshdream
Posts: 947 Forumite


Hi folks,
All our downstairs radiators are drop feeds and none had drain off valves. I am gradually replacing and upgrading the pipework and draining the system down is a pain to say the least!
This weekend I have swapped to radiator valves with a drain off where I can (Angled Radiator Valve Drain Off CP 10mm | Toolstation), but there are 2 rads that I can't do. The existing valves are simply too close to the wall and there is no space to put the larger valves on. So I have been looking at alternatives and see if I can add something like this:
Drain !!!!!! 15mm | Stopcocks | Screwfix.com or Self-Cutting Drain !!!!!! Type A 15mm | Stopcocks | Screwfix.com
The problem is all the pipework is 10mm, all surface mounted. As I replace each rad I am hiding the pipes and using 15mm for the bits that are on show but in the meantime I can't find anything that I can use on the existing 10mm.
Could anyone help at all please? Is there a way to do this or a product that I am missing in my google searches? I don't mind what it looks like as these will eventually be replaced. I need to drain down again a couple of times over the next few weeks and want to make it easier if possible.
Also, before I twigged about the lack of drain offs I was a bit of a numpty. I added a lovely vintage column radiator with some pretty brass valves without thinking of draining it down again. I want to keep these in place, so can I just add this Drain !!!!!! 15mm | Stopcocks | Screwfix.com to one of the 15mm sections? I'm not sure if that is the right product though.
All comments appreciated as always. Thanks. :-)
All our downstairs radiators are drop feeds and none had drain off valves. I am gradually replacing and upgrading the pipework and draining the system down is a pain to say the least!
This weekend I have swapped to radiator valves with a drain off where I can (Angled Radiator Valve Drain Off CP 10mm | Toolstation), but there are 2 rads that I can't do. The existing valves are simply too close to the wall and there is no space to put the larger valves on. So I have been looking at alternatives and see if I can add something like this:
Drain !!!!!! 15mm | Stopcocks | Screwfix.com or Self-Cutting Drain !!!!!! Type A 15mm | Stopcocks | Screwfix.com
The problem is all the pipework is 10mm, all surface mounted. As I replace each rad I am hiding the pipes and using 15mm for the bits that are on show but in the meantime I can't find anything that I can use on the existing 10mm.
Could anyone help at all please? Is there a way to do this or a product that I am missing in my google searches? I don't mind what it looks like as these will eventually be replaced. I need to drain down again a couple of times over the next few weeks and want to make it easier if possible.
Also, before I twigged about the lack of drain offs I was a bit of a numpty. I added a lovely vintage column radiator with some pretty brass valves without thinking of draining it down again. I want to keep these in place, so can I just add this Drain !!!!!! 15mm | Stopcocks | Screwfix.com to one of the 15mm sections? I'm not sure if that is the right product though.
All comments appreciated as always. Thanks. :-)
0
Comments
-
1. I don't think there is such a thing as a 10 mm drain off. BES don't list one.
2. You could use a 10 10 15 reducing tee such as https://www.mepstock.co.uk/pipes-and-fittings/endfeed-fittings/10mm-x-10mm-x-15mm-end-feed-both-end-reducing-tee with a short length of 15 mm pipe and the type A drain valve you reference.
3. Avoid self cutting devices. They can leave a slug of copper in the pipework to rattle forever.
4. You can add the final stopcock you reference into 15 mm pipework, but:
4.1 You will probably need a 15 mm equal tee and a short length of pipe.
4.2 If you are soldering any fitting with a rubber washer (like your references), don't forget to remove the rubber part before soldering and put it back afterwards.2 -
Thank you, that is really helpful.0
-
is this style of drain off any shorter?
https://www.pegleryorkshire.co.uk/EN/Brands/Terrier/Domestic_Radiator_Valves/Radiator Valves/product/367_CPDLS_Angle_Pattern_with_Drain_Off/item/6010562 -
BUFF said:is this style of drain off any shorter?
https://www.pegleryorkshire.co.uk/EN/Brands/Terrier/Domestic_Radiator_Valves/Radiator Valves/product/367_CPDLS_Angle_Pattern_with_Drain_Off/item/6010564 -
Thank you, I will have a measure and see if one of those will fit. :-) If not, I can carry on the awkward way until I get round to those rooms.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.6K Banking & Borrowing
- 253.4K Reduce Debt & Boost Income
- 454K Spending & Discounts
- 244.6K Work, Benefits & Business
- 600K Mortgages, Homes & Bills
- 177.3K Life & Family
- 258.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards