Is boiler broken or suffering in cold weather
dander
Posts: 1,824 Forumite
Since the beginning of this week (ie when it got really cold) my boiler (vaillant condensing combi) has been losing pressure very fast. I'm topping it up at least once a day to keep the heat on. I can't find a leak anywhere. Popped outside to look at the condensate pipe and there's clearly loads of water coming out there - big old iceberg on the wall of the house underneath it.
Does anyone know if my problem is more likely a boiler fault that has just coincidentally showed up this week, and I need to call a repairman. Or is there something about the cold weather that could be causing the boiler to spit out water? I'm guessing repairmen are not very available right now!
Does anyone know if my problem is more likely a boiler fault that has just coincidentally showed up this week, and I need to call a repairman. Or is there something about the cold weather that could be causing the boiler to spit out water? I'm guessing repairmen are not very available right now!
0
Comments
-
You have to check another pipe - pressure relief discharge. The only ways water can escape from the system are leaks and pressure relief valve.dander said:Popped outside to look at the condensate pipe and there's clearly loads of water coming out there - big old iceberg on the wall of the house underneath it.
2 -
At a guess, I'd suspect the expansion vessel has sprung a leak internally. Unfortunately, to replace this on many boilers will require a Gas Safe engineer. You should be able to find one locally, but you may well have to wait a few days as they are very busy (and charging extra for emergency call outs).If the boiler is still under warranty, it would be worth giving Vaillant a call and see if they can sort out a repair quickly.Any language construct that forces such insanity in this case should be abandoned without regrets. –
Erik Aronesty, 2014
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
ah, yes, it's the pressure relief pipe with the iceberg underneath.grumbler said:
You have to check another pipe - pressure relief discharge. The only ways water can escape from the system are leaks and pressure relief valve.dander said:Popped outside to look at the condensate pipe and there's clearly loads of water coming out there - big old iceberg on the wall of the house underneath it.0 -
10 years old, so no warranty. I'll get someone booked in now I know it won't magically mend itself when the weather warms up. Boiler still works as long as I just keep on topping it up so at least I won't go cold :-)FreeBear said:At a guess, I'd suspect the expansion vessel has sprung a leak internally. Unfortunately, to replace this on many boilers will require a Gas Safe engineer. You should be able to find one locally, but you may well have to wait a few days as they are very busy (and charging extra for emergency call outs).If the boiler is still under warranty, it would be worth giving Vaillant a call and see if they can sort out a repair quickly.0 -
In this case FreeBear's diagnosis is correct - expansion vessel. However, it possibly just needs recharging, not replacing.dander said:
ah, yes, it's the pressure relief pipe with the iceberg underneath.grumbler said:
You have to check another pipe - pressure relief discharge. The only ways water can escape from the system are leaks and pressure relief valve.dander said:Popped outside to look at the condensate pipe and there's clearly loads of water coming out there - big old iceberg on the wall of the house underneath it.
0 -
But it could also be a faulty or sticking PRV?No free lunch, and no free laptop
0 -
macman said:But it could also be a faulty or sticking PRV?
Quite possibly both. Expansion vessel fails. System over-pressurises and water is expelled through the PRV. But the water is full of muck from the heating system, which lodges in the valve, so it doesn't close again properly.
If it sticks, force it.
If it breaks, well it wasn't working right anyway.0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.2K Banking & Borrowing
- 253.6K Reduce Debt & Boost Income
- 454.3K Spending & Discounts
- 245.2K Work, Benefits & Business
- 600.9K Mortgages, Homes & Bills
- 177.5K Life & Family
- 259.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards