Rules for bathroom fan heaters

So I've inherited these in the bungalow and while ugly they are great for the shoulder season on a cold morning/evening when the heating isn't on.

Now I finally have people offering to do the bathroom I'm looking at potentially having fitted cupboards which are where the fan is. Far side from the bath/shower and I would need to move it.

Are they still legal and could I put it closer to the bath - opposit end to the shower or taps. I could perhaps squeeze it in a corner over the loo if I had to but not so useful.

But wondered if they are still legal so it could be repositioned with rewire or if I would fall into any problems with moving it?

I can rise and shine - just not at the same time!

viral kindness .....kindness is contageous pass it on

The only normal people you know are the ones you don’t know very well


Comments

  • daveyjp
    daveyjp Posts: 13,314 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    They are legal, electrical installation regulations will dictate where it can and can't be installed in terms of distance from showers, baths etc and will need to be hard wired into a fused spur.
  • twopenny
    twopenny Posts: 7,098 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Thanks Davey, thats how it is at the moment.

    I'll try and get some advice on siting it near the lounging end of the bath and cost.

    Not beautiful but really heavenly on a cold morning. Compromise for comfort and convenience over style.

    I was afeared that they were banned by now.
    Was going to remove them when I viewed until I found why they were used during the 'stay in place' during the pandemic.

    I can rise and shine - just not at the same time!

    viral kindness .....kindness is contageous pass it on

    The only normal people you know are the ones you don’t know very well


  • grumbler
    grumbler Posts: 58,629 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 29 November 2022 at 7:59PM
    daveyjp said:
    They are legal, electrical installation regulations will dictate where it can and can't be installed in terms of distance from showers, baths etc and will need to be hard wired into a fused spur.
    And, most likely, have to be switched on/off with a pull-cord switch or from outside of the bathroom.
    I have a nice one from Lidl that I really like
    bordo librarsi incompleto set manicure elettrico lidl accappatoio alcova  Pantano


  • ka7e
    ka7e Posts: 3,116 Forumite
    Part of the Furniture 1,000 Posts Photogenic
    Bathroom heaters have to have an IP rating, depending how close they are to a water source (zones). Explanatory article here - https://www.plumbworld.co.uk/bathroom-zones-ip-rating-infopage
    "Cheap", "Fast", "Right" -- pick two.
  • Your electrician will be familiar with the 18th edition regs and the zones in your bathroom where it can be located.
    Signature on holiday for two weeks
  • twopenny
    twopenny Posts: 7,098 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Electrician. Aww it's taken 2yrs to get a plumber!

    I can rise and shine - just not at the same time!

    viral kindness .....kindness is contageous pass it on

    The only normal people you know are the ones you don’t know very well


  • ka7e said:
    Bathroom heaters have to have an IP rating, depending how close they are to a water source (zones). Explanatory article here - https://www.plumbworld.co.uk/bathroom-zones-ip-rating-infopage
    Your link refers to the older 17th edition rules. The 18th edition now has an "outside zone" but this is limited to "outside zone part 1" which is 3 metres from the outside edge of the bathtub. In the majority of UK homes, this is likely to be the other side of the room or the ceiling. Outwith zone 1 and 2 but within the outside zone part 1, you can have 240v devices but they must be protected by a 30ma RCD.

    https://18th-edition.org.uk/bathroom-zones/


    Signature on holiday for two weeks
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Why would they be 'banned'? As long as they're hard wired, pull-cord operated and correctly zoned, they are no more dangerous than any other electrical heater in a bathroom.
    No free lunch, and no free laptop ;)
  • twopenny
    twopenny Posts: 7,098 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Why 'Banned?
    Because I'm old and I've seen and increasing number of things that have been used safely over the years banned or about to be so I expect the worst.

    I can rise and shine - just not at the same time!

    viral kindness .....kindness is contageous pass it on

    The only normal people you know are the ones you don’t know very well


Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.7K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 452.9K Spending & Discounts
  • 242.7K Work, Benefits & Business
  • 619.4K Mortgages, Homes & Bills
  • 176.3K Life & Family
  • 255.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.