Rules for bathroom fan heaters
I can rise and shine - just not at the same time!
viral kindness .....kindness is contageous pass it on
The only normal people you know are the ones you don’t know very well
Comments
-
They are legal, electrical installation regulations will dictate where it can and can't be installed in terms of distance from showers, baths etc and will need to be hard wired into a fused spur.
1 -
Thanks Davey, thats how it is at the moment.
I'll try and get some advice on siting it near the lounging end of the bath and cost.
Not beautiful but really heavenly on a cold morning. Compromise for comfort and convenience over style.
I was afeared that they were banned by now.
Was going to remove them when I viewed until I found why they were used during the 'stay in place' during the pandemic.I can rise and shine - just not at the same time!
viral kindness .....kindness is contageous pass it on
The only normal people you know are the ones you don’t know very well
0 -
daveyjp said:They are legal, electrical installation regulations will dictate where it can and can't be installed in terms of distance from showers, baths etc and will need to be hard wired into a fused spur.And, most likely, have to be switched on/off with a pull-cord switch or from outside of the bathroom.I have a nice one from Lidl that I really like
1 -
Bathroom heaters have to have an IP rating, depending how close they are to a water source (zones). Explanatory article here - https://www.plumbworld.co.uk/bathroom-zones-ip-rating-infopage
"Cheap", "Fast", "Right" -- pick two.1 -
Your electrician will be familiar with the 18th edition regs and the zones in your bathroom where it can be located.Signature on holiday for two weeks1
-
Electrician. Aww it's taken 2yrs to get a plumber!
I can rise and shine - just not at the same time!
viral kindness .....kindness is contageous pass it on
The only normal people you know are the ones you don’t know very well
0 -
Your link refers to the older 17th edition rules. The 18th edition now has an "outside zone" but this is limited to "outside zone part 1" which is 3 metres from the outside edge of the bathtub. In the majority of UK homes, this is likely to be the other side of the room or the ceiling. Outwith zone 1 and 2 but within the outside zone part 1, you can have 240v devices but they must be protected by a 30ma RCD.ka7e said:Bathroom heaters have to have an IP rating, depending how close they are to a water source (zones). Explanatory article here - https://www.plumbworld.co.uk/bathroom-zones-ip-rating-infopage
https://18th-edition.org.uk/bathroom-zones/
Signature on holiday for two weeks1 -
Why would they be 'banned'? As long as they're hard wired, pull-cord operated and correctly zoned, they are no more dangerous than any other electrical heater in a bathroom.No free lunch, and no free laptop
0 -
Why 'Banned?Because I'm old and I've seen and increasing number of things that have been used safely over the years banned or about to be so I expect the worst.
I can rise and shine - just not at the same time!
viral kindness .....kindness is contageous pass it on
The only normal people you know are the ones you don’t know very well
1
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.9K Banking & Borrowing
- 253.9K Reduce Debt & Boost Income
- 454.7K Spending & Discounts
- 246K Work, Benefits & Business
- 602.1K Mortgages, Homes & Bills
- 177.8K Life & Family
- 259.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards