How much does DNO approval cost / is it worth it for my system
Options
Comments
-
Thanks - perhaps this installer is just busy and was trying to find a way to fob me off.0
-
ccbrowning said:Is there a range? I spoke to an installer who told me to speak to the DNO first and it could be up to £9k, to go over 3.68kW. I have an existing 3.4kW system and want to expand and add a battery.
Can you just get an inverter that limits export?
https://www.enwl.co.uk/get-connected/apply-for-a-new-connection/generation-and-storage/micro-generation-and-storage-connections/Integrated micro-generation and storage
Working in partnership with the ENA, a relaxation was written into G99. This relaxation has primarily been developed where a customer is wishing to combine a G83/G98 generator with an Energy Storage Device.
To qualify, the following conditions must be met:
- Total generation capacity installed should not exceed 7.36KW (including battery storage)
- All generators should be connected via a Type approved G83/G98 protection device
- The maximum export should be limited to 3.68KW per phase utilising a Type approved EREC G100 device
- The system should not generate during a power-cut (island mode)
G99 is like a check list of things that if you can demonstrate you comply with, the DNO won't charge you for them to check. Less than 1MW is category A. Batteries are currently exempt from some of the items on the list.
I think the list given is to allow installations that would normally be G99, to be treated at G98. So you won't be charged if you can say yes to the checklist: combined battery storage and pv inverter doesn't exceed 7.36kW; MSC installation; G100 compliant export limitation device; don't operate in island mode.
G100 is the guidance for export limitation schemes (in the way that G98 applies to domestic scale generation). It is usually installed where the inverter can export more than the allowed capacity.
If your battery and pv are DC connected, the inverter will limit the export so you won't need additional export limitation.
Though I suspect the wording above is to allow people with FITs installations to add batteries without compromising their FITs generation payments - i.e. they will be AC coupled.
I'm not sure what the £9k would be for unless it is as @ABrass says and it is to upgrade your single phase supply to 3 phase.
How big a battery are you looking to connect? (Sorry if you've said above).
Edit: if in doubt, give them a call and ask to speak to an engineer.4.3kW PV, 3.6kW inverter. Octopus Agile import, gas Tracker. Zoe. Ripple x 3. Cheshire2 -
Thanks @70sbudgie! We're looking at adding 9.5kW of battery storage and doubling our PV to take up into the 7.x range.0
-
ccbrowning said:Thanks @70sbudgie! We're looking at adding 9.5kW of battery storage and doubling our PV to take up into the 7.x range.
With a set up of that size (the latter) you may need a 3 phase system!4.3kW PV, 3.6kW inverter. Octopus Agile import, gas Tracker. Zoe. Ripple x 3. Cheshire0 -
A 9.5kWh storage - https://www.deegesolar.co.uk/givenergy_9-5kwh_battery/
We won't send much to the grid at all due to the load, except maybe some summer days if we don't use the computers (100% electric house, gshp, I work in IT, etc.)1 -
Our installer charged a total of £175 for DNO application (G99) but that has also included insurance fee (to cover protection of our 1st payment deposit & we have the policy).
Seen it all, done it all, can't remember most of it.1 -
ABrass said:ccbrowning said:Is there a range? I spoke to an installer who told me to speak to the DNO first and it could be up to £9k, to go over 3.68kW. I have an existing 3.4kW system and want to expand and add a battery.
Can you just get an inverter that limits export?
https://www.enwl.co.uk/get-connected/apply-for-a-new-connection/generation-and-storage/micro-generation-and-storage-connections/Integrated micro-generation and storage
Working in partnership with the ENA, a relaxation was written into G99. This relaxation has primarily been developed where a customer is wishing to combine a G83/G98 generator with an Energy Storage Device.
To qualify, the following conditions must be met:
- Total generation capacity installed should not exceed 7.36KW (including battery storage)
- All generators should be connected via a Type approved G83/G98 protection device
- The maximum export should be limited to 3.68KW per phase utilising a Type approved EREC G100 device
- The system should not generate during a power-cut (island mode)
Many modern inverters can cap export, it's a common feature now.Mart. Cardiff. 8.72 kWp PV systems (2.12 SSW 4.6 ESE & 2.0 WNW). 20kWh battery storage. Two A2A units for cleaner heating. Two BEV's for cleaner driving.
For general PV advice please see the PV FAQ thread on the Green & Ethical Board.2 -
I have heard of some sort of grant that completely covers the cost to upgrade to 3 phase (in the NW area). But I haven't found anything to back up the one comment.4.3kW PV, 3.6kW inverter. Octopus Agile import, gas Tracker. Zoe. Ripple x 3. Cheshire1
-
Forget about 3 phase. Dno approval for g99 is generally free for what you are asking for. Phone them - they won't bite. Mine, through London power networks, for a very similar system (see below my message) was free and they generally are.The reason the DNO express the possibility of charges is for situations where much bigger and more grown-up things are taking place requiring site assessments, etc.More importantly, your inverter is way too small there. If there is a potential degradation or mismatching issue due to the different aspects, get a solaredge optimiser on each panel. Sorted.London. 6.4kwh system, South facing. 16 Hyundai 400kw all black panels w/ optimisers, 6kw Solaredge HD Wave inverter, Solar Iboost with two immersion heaters on one 240l hw tank. Octopus Flux. Ivar 5 Wood Burning Stove. Leaf 62kwh plus Zappi. Two chickens: 1 Light Sussex, 1 Speckled Rock. Omlet walk-in run. Approx 1.5 eggs per day egg generation rate using Marriage's organic layers pellets.1
-
70sbudgie said:I have heard of some sort of grant that completely covers the cost to upgrade to 3 phase (in the NW area). But I haven't found anything to back up the one comment.
80-100A single phase supplies are capable of coping with a lot of PV / BEV / batt / HP issues, but 3phase would make life easier, and allow for growth - just like the bigger PV and DNO permission issues that crop up on here all the time. Going back 10+yrs, a good/large PV install was 4kWp, with 250Wp panels. Now we are closing in on 400Wp of a similar size, that lifts the figure to 6.4kWp, which is just a bit too big for a 3.68kW cap, and in my situation with smaller roofs, but two (E/W) my 5.58kWp scaled up would be about 9kWp today.
So there may well be forms of support somewhere for transitioning, as you seem to recall.Mart. Cardiff. 8.72 kWp PV systems (2.12 SSW 4.6 ESE & 2.0 WNW). 20kWh battery storage. Two A2A units for cleaner heating. Two BEV's for cleaner driving.
For general PV advice please see the PV FAQ thread on the Green & Ethical Board.3
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.1K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599.1K Mortgages, Homes & Bills
- 177K Life & Family
- 257.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards