Lux hybrid 3.6 and 2x4.8 storage. Only using 3.2kw of discharge.
Options

arms
Posts: 18 Forumite

New install and noticing when the load is on the battery we are are maxing at 3.2kw discharge and taking the rest from grid. We hit 3.6 with solar.

0
Comments
-
Is this normal? Do I have a setting wrong?0
-
Here’s with the immersion on.0
-
What's the maximum discharge rate on your Pylontechs? It could be 32A each, which would be 1.6kW each at a nominal 50V but a bit less as the voltage drops?
N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!0 -
My battery cannot manage a 3 kW discharge (or my inverter won't let it). The most it has managed today is 2.5 kW and I think that's typical.Reed0
-
I’m not sure if I have the UP5000 (50A) or the US5000 (80A) will check tomorrow.0
-
Reed_Richards said:My battery cannot manage a 3 kW discharge (or my inverter won't let it). The most it has managed today is 2.5 kW and I think that's typical.0
-
After more digging, the continuous discharge rate of a US5000 is 2.4kw. So should total be 4.8kw (limited to 3.6kw due to inverter)?0
-
Taken the manual on the Luxpower site.
0 -
arms said:Taken the manual on the Luxpower site.But look at the line above - max charge/discharge current 66A.Power is voltage x current. In order to get 3600W at 66A, you need a battery voltage of 54.5V.In the image you posted with your immmersion on, your battery voltage is only 49.1V so the maximum possible discharge at that time is 3240W, not 3600W. (3106W is 63.3A at 49.1V, so it's still slightly less than nominal, but you'd need to know how the rated conditions for the inverter compare to the actual conditions in your installation regarding temperature etc.)N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!1 -
QrizB said:arms said:Taken the manual on the Luxpower site.But look at the line above - max charge/discharge current 66A.Power is voltage x current. In order to get 3600W at 66A, you need a battery voltage of 54.5V.In the image you posted with your immmersion on, your battery voltage is only 49.1V so the maximum possible discharge at that time is 3240W, not 3600W. (3106W is 63.3A at 49.1V, so it's still slightly less than nominal, but you'd need to know how the rated conditions for the inverter compare to the actual conditions in your installation regarding temperature etc.)0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.9K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.9K Work, Benefits & Business
- 598.8K Mortgages, Homes & Bills
- 176.9K Life & Family
- 257.2K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards