Solar Battery output/discharge rate

180 Posts


Can someone who is familiar with Givenergy answer this question please?
If I understand correctly Givenergy Giv-Bat 5.2kwh has a discharge rate of 3kWh (51.2v x 60A = 3kWh)
If I have 2 Givenergy Giv-Bat 5.2kwh paired, would the output/discharge rate be doubled to 6kWh, or it doesn't work like that?
Reading the Givenergy spec sheet I can't seem to see it.
I've been quoted both Solaredge and Givenergy, Solaredge has a higher battery discharge rate than Givenergy.
Givenergy seems to be significantly cheaper than Solaredge but I have read positive things with Givenergy so can't quite decide yet.
Having an EV charger, and Air conditioning system at home I would assume I need the higher battery/inverter discharge rate.
Thanks
If I understand correctly Givenergy Giv-Bat 5.2kwh has a discharge rate of 3kWh (51.2v x 60A = 3kWh)
If I have 2 Givenergy Giv-Bat 5.2kwh paired, would the output/discharge rate be doubled to 6kWh, or it doesn't work like that?
Reading the Givenergy spec sheet I can't seem to see it.
I've been quoted both Solaredge and Givenergy, Solaredge has a higher battery discharge rate than Givenergy.
Givenergy seems to be significantly cheaper than Solaredge but I have read positive things with Givenergy so can't quite decide yet.
Having an EV charger, and Air conditioning system at home I would assume I need the higher battery/inverter discharge rate.
Thanks
0
Latest MSE News and Guides
Childcare budget boost
More support for children from nine months and those on Universal Credit
MSE News
Replies
The Giv-HY 5.0 inverter is capable of 6500W DC power, I assume it's Battery DC to Inverter DC to Consumer unit AC.
Giv-Bat 5.2kwh is only capable of 3000W.
Even if Giv-HY 5.0 inverter is capable of 6500W DC power, it still won't pull that much if there are 2 batterys?
If the battery is limited to a max of 3000W discharge this will then be the limiting factor. So with two inverters and two batteries ( one coupled to each) maximum theoretical discharge will be 6kW (6000W).
Would the batterys run at full discharge capacity rate, so if there were 2 x Giv-Bat 5.2kwh both discharging at 3kwh to the inverter, would the Giv-HY 5.0 inverter be receiving a combined total of 5kWh from both batteries?
If it isn't the case, bit confused to why the batteries would discharge at half the capacity if there are 2 batterys.
Max DC Power 6500W (incoming from battery and solar PV)
The inverter it's max AC discharge rate is 5000W (Nominal AC Output Power):
https://www.givenergy.co.uk/pdf/Version 2.0/Hybrid Inverter.pdf
Someone else might be able to confirm as my dual inverter and batteries haven't been installed yet.
Normally battery discharge above 1C will significantly affect capacity.
1C is roughly your battery capacity discharged in an hour and most manufacturers limit current to prevent disharge above 1C. This reduces customers getting disappointed due to reduced capacity and higher installation costs.
Adding two batteries will only provide increased capacity and not increased output, which is dependent on your inverter capacity.
Givenergy AC coupled is limited to 3.5KWh or 3000VA continuous. hybrid inverters seems to have higher continous rating 5000VA. Might want to look into the larger inverter if you are planning to run multiple inductive loads.