    edited 27 April 2022 at 6:47AM
    "Advanced Weather Compensation"?  I have seen that term used to describe Weather Compensation" and "Load Compensation" but these are actually separate things (and my Atag gas boiler bought in 1998 could do both).  There is an interesting article on Low Temperature Heating Systems here: https://www.heatgeek.com/benefits-of-low-temprature-heating-systems/ .  As usual with Heat Geek it is OTT  but if the chart of boiler efficiency against return water temperature is to be believed you need the return water to be at about 15 C to achieve your 98% efficiency in which case you certainly do need Weather Compensation.

    Edit:  another reference with the same diagram: https://www.purmo.com/au/clever/guide-the-increasing-use-of-low-temperature-water-systems.htm   
    Reed
  • Screwdriva
    Screwdriva Posts: 1,367 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 27 April 2022 at 12:07PM
    "Advanced Weather Compensation"?
    https://viessmanndirect.co.uk/files/8e57dbc7-8a10-4065-bcc6-a27700ee752a/weather_comp.pdf

    Seems like a more intuitive use of weather and room temperature inputs to me. Only available on the 200-W.
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • BUFF
    BUFF Posts: 2,185 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper

    ...Given the 200-W can modulate below 2kW in theory and has advanced weather compensation and is more efficient and combined with the increase in radiator surface area + UFH, I'm quite optimistic we will see a real world savings % in the double digits over an already efficiency setup. 
    I think you may be being over optimistic and double-counting some of the beneficial features.  The best you can achieve with a gas boiler is 100% efficiency.  Your old boiler, operated at 50/30 might well have achieved >90% efficiency.  If the new one has a SCOP of 0.98 (i.e. 98% efficiency) then that is probably because it has all the other features and faculties you list; they are necessities to the performance, not extras.
    You may be right on my level of optimism. What is clear is that the Viessmann boiler has a superior modulation ratio and advanced weather compensation, which my Greenstar 18Ri boiler does not. Installing UFH and increasing radiator surface area are additional improvements proven to improve low flow temperature heating.

    I'll be sure to report back with real world consumption numbers.
    You will have to bear in mind when comparing future system consumption to present system/this year consumption that this has been an unusually mild winter (at least in Glasgow) - my gas consumption is down ~30%.
  • Reed_Richards
    Reed_Richards Posts: 5,148 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper

    Seems like a more intuitive use of weather and room temperature inputs to me. Only available on the 200-W.
    Strangely there is no mention of Load Compensation and I cannot see an indication  that this function is performed.  If your desired room temperature is say 21 C and the actual temperature is 18 C then you want the boiler to work quite hard.  But when the actual temperature approaches the desired temperature , say 20.9 C, you want the boiler to modulate its output right down so it maintains just enough output to get to 21 C then maintain a steady temperature.  This will give you a boiler flow temperature that is completely stable (for as long as the outside temperature remains the same). 
    Reed
  • Screwdriva
    Screwdriva Posts: 1,367 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    BUFF said:
    You will have to bear in mind when comparing future system consumption to present system/this year consumption that this has been an unusually mild winter (at least in Glasgow) - my gas consumption is down ~30%.
    Yes, of course. In the thread I've linked, I compare only months with near identical average temperatures. 
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Reed_Richards
    Reed_Richards Posts: 5,148 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    The top chart (from your referenced document) makes no sense and the bottom one worries me because you never appear to achieve the steady boiler flow temperature that Load Compensation would give you.




    Reed
  • ABrass
    ABrass Posts: 1,005 Forumite
    Part of the Furniture 500 Posts Name Dropper
    The top chart (from your referenced document) makes no sense and the bottom one worries me because you never appear to achieve the steady boiler flow temperature that Load Compensation would give you.




    Perfect weather compensation wouldn't give you a steady boiler temperature, it would increase and decrease to match the rate of heat loss, which in turn would vary because of external temperature.

    The graphs are a bit silly, Apparently before you have weather compensation you like 10 degree rooms but afterwards you punch it up to 20.
    8kW (4kW WNW, 4kW SSE) 6kW inverter. 6.5kWh battery.
  • Cardew
    Cardew Posts: 29,056 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Rampant Recycler
    I have weather compensation on my Viessmann 100 boiler - so not advanced weather compensation.

    I wonder how much it actually saves? Viessmann state UP TO 15% but of course 'up to' covers a saving of 0.0001%!!
  • Screwdriva
    Screwdriva Posts: 1,367 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    This is the most thorough review of the boiler I could find. 

    https://www.heatgeek.com/viessmann-vitodens-200-boiler-review/
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • Reed_Richards
    Reed_Richards Posts: 5,148 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    they also offer external controls and room sensors in the form of the Vitotrol 200 and Vitotrol 300. These both give the optimum solution of placing a room influence % on your weather compensated control.

    It looks like you would need the Vitrotrol 300A to give you control over your upstairs and downstairs zones and the ability to program and control your hot water.  Any other controller and you might be in difficulty because:
     there is an Opentherm module available opening it up to third-party controls. However, this module is hard to obtain in the UK and is not supported by Viessmann UK.


    Reed
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349K Banking & Borrowing
  • 252.4K Reduce Debt & Boost Income
  • 452.7K Spending & Discounts
  • 241.9K Work, Benefits & Business
  • 618.5K Mortgages, Homes & Bills
  • 176.1K Life & Family
  • 254.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.