Electrics cutout after drilling through ceiling but didn't hit anything

Hi all,

I was trying to install a ceiling light yesterday and my drill slipped and went fully into the ceiling. 10 minutes later the RCCB cut out. Turn it back on and then does the same 5 minutes later.

Thinking I hit a socket wire upstairs I isolated the upstairs socket circuit. The RCCB cuts out again.

Upstairs, rip up the carpet, rip up the board and I find my hole and it's hit nothing but fresh air.

Leave electrics off for an hour and turn it back on and it's remained on over night (with the lighting circuit still isolated as the light is still unplugged). We unplugged everything and are in the process of checking every single appliance. However, the absolute coincidence of that is extreme unlikely, in my opinion. 

I have some questions:

1) What could have been doing it?
2) Why has it seemed to have stopped (for now)? 
3) Is it possible for plugged-in items to trip it even though they're not being used (such as a drill)
4) I did kind of have to 'yank' the pendant a little to get off through years of paint applied to it. Is it possible to have physically pulled something? (even though it's remained isolated?

I appreciate any advice.

TIA
«1

Comments

  • rob7475
    rob7475 Posts: 968 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    The fact that the RCCB tripped 10 minutes after you drilled into the ceiling suggests that you didn't hit anything otherwise it would have tripped immediately.

    I'd check the wiring into your pendant and make sure nothing's come loose in there. If it's not that, it's possible it's your drill that's tripping it - has it tripped at all since your drill's been unplugged?
  • tacpot12
    tacpot12 Posts: 9,419 Forumite
    Ninth Anniversary 1,000 Posts Name Dropper
    I'd also check the socket where the drill was plugged in. A loose connection in their might have been disturbed when you uunplugged your drill. 
    The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.
  • Ben1989
    Ben1989 Posts: 470 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    I initially thought I hadn't hit a wire because the drill was still in my hand and not launched to the other end of the hall haha.

    I actually removed the pendant and it's just bare wires at the moment.

    Could the drill trip it even though it wasn't being used at the time but plugged in? It has in fact not tripped since being unplugged. I keep mithering the wife for a cordless drill.

    Thanks tacpot12, I'll give it a check. 
  • Eldi_Dos
    Eldi_Dos Posts: 2,351 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    When you pulled the pendent down could the cable have pulled another cable hard against a sharp edge affecting it's insulation.
  • Ben1989
    Ben1989 Posts: 470 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    I'm not sure I think the lighting circuit has it's on conduit and also it's remained isolated. I know nothing however,
  • FreeBear
    FreeBear Posts: 18,306 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    Ben1989 said: I'm not sure I think the lighting circuit has it's on conduit and also it's remained isolated. I know nothing however,
    "Isolating" the lighting circuit by way of the MCB only kills power on the live side (line). The neutral is still connected, and if the RCCB detects any leakage current on this neutral, it will trip.

    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • Ben1989
    Ben1989 Posts: 470 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    FreeBear said:
    Ben1989 said: I'm not sure I think the lighting circuit has it's on conduit and also it's remained isolated. I know nothing however,
    "Isolating" the lighting circuit by way of the MCB only kills power on the live side (line). The neutral is still connected, and if the RCCB detects any leakage current on this neutral, it will trip.

    So it could still be the lighting circuit that could be tripping it?
  • FreeBear
    FreeBear Posts: 18,306 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    Ben1989 said:
    FreeBear said:
    Ben1989 said: I'm not sure I think the lighting circuit has it's on conduit and also it's remained isolated. I know nothing however,
    "Isolating" the lighting circuit by way of the MCB only kills power on the live side (line). The neutral is still connected, and if the RCCB detects any leakage current on this neutral, it will trip.

    So it could still be the lighting circuit that could be tripping it?
    If there is a fault on the lighting circuit, then yes it could still cause the RCCB to trip.
    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • Ben1989
    Ben1989 Posts: 470 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    Right okay. Thanks FreeBear. Drill seems to not be the cause
  • Ben1989
    Ben1989 Posts: 470 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    Cracked it!

    The neutral and earth making contract were cutting it out. I just tested it
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.2K Banking & Borrowing
  • 253.6K Reduce Debt & Boost Income
  • 454.3K Spending & Discounts
  • 245.3K Work, Benefits & Business
  • 601K Mortgages, Homes & Bills
  • 177.5K Life & Family
  • 259.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.