Type of wire needed for Oven and Microwave oven

Hi
What type of electric wire is needed for in built Oven and Microwave oven.
We dont wish to get into circuit problems,appliance breakdowns or trippings.
Two sparkies we got to get the work done said any type of wires would do.However previously wheneven we got microwave and oven on at same time,we used to get frequent circuit breaker tripping.
Many Thanks

Comments

  • FreeBear
    FreeBear Posts: 18,366 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    edited 12 March 2022 at 7:19PM
    Assume a 3KW oven, and a 1000w microwave (which will be around 1.5KW input power), you'll be drawing a maximum of ~19A. Problem with a microwave is it has a ruddy great transformer inside which has a very high startup load which could be causing your MCB to trip. A type C MCB should solve any nuisance tripping when turning the microwave on. Changing the wiring isn't going to fix the problem on its own.
    What rating of MCB (and type) do you currently have fitted ?
    Any language construct that forces such insanity in this case should be abandoned without regrets. –
    Erik Aronesty, 2014

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • FaceHead
    FaceHead Posts: 737 Forumite
    500 Posts Second Anniversary Name Dropper
    Is it the MCB or the RCD that trips. That is the breaker that protects just that circuit, or one that has other things on it too (e.g. upstairs lights)

    Well it's simply not the case that "any type of wire will do". What are the ratings of the appliances? (Freebear provides some sensible guesses, but let's hear what the appliances you've chosen actually are).

    Is anything else going on that circuit too? e.g. Other built in appliances.

    Realistically you'll need a 32A ring in 2.5mm twin and earth. It would be able to take another couple of appliances too.
  • Ectophile
    Ectophile Posts: 8,405 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    What sort of electrician would say "any type of wires would do"?  That's just asking for trouble.  You need to look at the rating plate of the oven, at least.

    A single oven will often take 3kW, and can have a 13A plug on it.  Double ovens need more, maybe 16A or 20A.

    Then, what sort of circuit - a ring or a radial?  Both on the same circuit, or a separate radial for each?  The answer could come out anything between 1.5mm² up to 4mm².  Whatever cable you use has to be adequately protected by the breaker at the consumer unit.




    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
  • Risteard
    Risteard Posts: 2,000 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    FreeBear said:
    Assume a 3KW oven, and a 1000w microwave (which will be around 1.5KW input power), you'll be drawing a maximum of ~19A. Problem with a microwave is it has a ruddy great transformer inside which has a very high startup load which could be causing your MCB to trip. A type C MCB should solve any nuisance tripping when turning the microwave on. Changing the wiring isn't going to fix the problem on its own.
    What rating of MCB (and type) do you currently have fitted ?

    There shouldn't be any huge inrush current from a microwave. There is absolutely no reason not to use a Type B circuit breaker. These should never simply be replaced with Type C or Type D devices either, without understanding the effect this has on the maximum Earth fault loop impedance permitted to cause operation within the required times.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.4K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.3K Work, Benefits & Business
  • 604K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.