Central heating boiler losing pressure (again)
Comments
-
Granny_98 said:Unless there is the right access (rare) it's not possible to replace the expansion vessel in that WB boiler without removing the boiler entirely from the wall. Not a quick job which is why the replacements are usually put external to the boiler.
Given the 5 week time lag it seems that the expansion vessel was merely repressurised and it then lost it's pressure over the following 5 weeks. From then on every time the boiler heats up it (the heating system) over-pressurises and forces water out of the safety valve. Pressure drops, you top up, repeat....
It sounds like you use the original installer for servicing so call them about the problem and see what they say/suggest. If it is the expansion vessel or boiler that's at fault you don't want to be paying but if it is a leak then it needs finding and sorting.
Sorry I can't think of anything profound, clever or witty to write here.0 -
This may be completely irrelevant but just in case it's not, see my post here:
https://forums.moneysavingexpert.com/discussion/comment/78806265#Comment_78806265
0 -
Ah ok but in your 1st post you said EV "supposedly replaced" and you implied he'd not been that long on the 2nd visit.0
-
KittenChops said:This may be completely irrelevant but just in case it's not, see my post here:
https://forums.moneysavingexpert.com/discussion/comment/78806265#Comment_78806265
No other form of heating
1 -
KittenChops said:This may be completely irrelevant but just in case it's not, see my post here:
https://forums.moneysavingexpert.com/discussion/comment/78806265#Comment_78806265
Your issue sees to have been about the gas supply pressure, and not 'system', so sadly not relevant to this problem.
0 -
Bendy_House said:KittenChops said:This may be completely irrelevant but just in case it's not, see my post here:
https://forums.moneysavingexpert.com/discussion/comment/78806265#Comment_78806265
Your issue sees to have been about the gas supply pressure, and not 'system', so sadly not relevant to this problem.
1 -
Granny_98 said:Ah ok but in your 1st post you said EV "supposedly replaced" and you implied he'd not been that long on the 2nd visit.I have read (on here) about certain WB boilers having their EV's located at the back of the boiler, so necessitating a boiler-off-the-wall task to have it replaced. That sounds quite major, but I can see it actually being less involved that swapping some internal parts; isolate all pipes at the bottom of the boiler, disconnect wiring, disconnect flue, and lift the darned thing off...Mind you, isn't lifting off and replacing a boiler a 2-person job? In which case, did this person actually replace the EV as claimed?(But, I don't know if the EV is behind the boiler, and if it is a 2-person job.)In any case, a faulty EV being responsible for the pressure loss would also require the pressure to soar (as it would) and for the excess system water to be dumped out the discharge pipe - which it seemingly wasn't.Because you haven't collected any water in the 'copper' plastic bag, this unfortunately remains a mystery to me, Granny. :-(0
-
Oh, if when you get them back (well done for keeping the warranty going
) they say it is a faulty EV and want to fit an external one, suggest that they first cover this EV with vaseline, because you will be sticking it where the... ('admin deleted...')
0 -
Bendy_House said:And are you up for turning a couple of valves if it comes to it? The boiler is shut off at night - power fully off - and the F&R valves given a quarter-turn to close them. If the pressure still drops, the leak is from within the boiler.1
-
If your boiler has a 10 year warranty and it has been serviced regularly then I would be asking WB to resolve the issue. They have their own team of engineers and they carry most parts on the van. I called them out to my boiler last year and they happily replaced the fan and the syphon. The service visit cost me nothing.1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 352.1K Banking & Borrowing
- 253.6K Reduce Debt & Boost Income
- 454.2K Spending & Discounts
- 245.1K Work, Benefits & Business
- 600.8K Mortgages, Homes & Bills
- 177.5K Life & Family
- 258.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards