price to convert TT electric supply to TNCS supply

hi there
i need to ring the electric company next week to get them in to check if its possible to convert my TT pole supply to TNCS
just wondering if any one has had it done recently & how much did it cost

«1

Comments

  • Risteard
    Risteard Posts: 1,951 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 16 October 2021 at 9:13AM
    gamston said:
    hi there
    i need to ring the electric company next week to get them in to check if its possible to convert my TT pole supply to TNCS
    just wondering if any one has had it done recently & how much did it cost

    You will also need to consider whether the Earthing conductor and main protective bonding conductors etc. are adequately sized. You should get an electrical contractor on board too. What is the reason for seeking to change from TT (Direct Earthing)? 

    Only the DNO can answer for their side as TN-C-S is generally PME which requires multiple Earthing connections of the PEN conductor. Only they know what work is required on their network. 
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • gamston
    gamston Posts: 693 Forumite
    Part of the Furniture 500 Posts
    Looking to move, so want to get the place into shape
    this place has never had an earth, I've lived here 40yrs and been ok, but want to sort before i put on market
  • dj1471
    dj1471 Posts: 1,969 Forumite
    Part of the Furniture 1,000 Posts Home Insurance Hacker!
    gamston said:
    this place has never had an earth, I've lived here 40yrs and been ok, but want to sort before i put on market
    Come again? If it’s TT then you have an earth rod, this is a perfectly acceptable form of earthing.

    Money would be better spent on upgrading the CU to add RCD protection, if not already present.
  • Risteard
    Risteard Posts: 1,951 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 17 October 2021 at 12:23AM
    dj1471 said:
    gamston said:
    this place has never had an earth, I've lived here 40yrs and been ok, but want to sort before i put on market
    Come again? If it’s TT then you have an earth rod, this is a perfectly acceptable form of earthing.

    Money would be better spent on upgrading the CU to add RCD protection, if not already present.

    TT will have RCD protection, otherwise there won't be any fault protection (previously referred to as protection against indirect contact) unless there is an extremely low impedance Earth path through the electrode and general mass of Earth (which there almost certainly won't be)!

    There may not be 30mA RCD additional protection (previously supplementary protection), however. It could be a time-delayed device which a much greater rated residual operating current.
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • gamston
    gamston Posts: 693 Forumite
    Part of the Furniture 500 Posts
    there is a RCD but no earth, never has been as far as i know
    yes could have earth rods but the cable run is not simple/easy, i don't want it just pegged to outside wall, want it run via loft/garage
    so i was thinking get the DNO out (thats free ?) to look and tell me if I can get PME, and cost, then i need a electrical contractor to fit earth from CU to DNO PME point and sign off
  • Section62
    Section62 Posts: 8,631 Forumite
    1,000 Posts Third Anniversary Name Dropper
    gamston said:

    there is a RCD but no earth, never has been as far as i know

    Are you sure it is an RCD?  With older installations there's a chance of finding voltage-operated ELCBs, which can look very similar, but function differently.  You'd still expect to find some system earthing, but it wasn't unknown in the past for the earthing to be achieved via the incoming water pipe or something similarly unsuitable.

    It would be very odd for an electrician to install an RCD in an everyday situation without first making sure the earthing arrangements were appropriate.  If there has been DIY work done in the past there could be other hurdles to overcome before you can get sign-off.

    gamston said:

    so i was thinking get the DNO out (thats free ?) to look and tell me if I can get PME, and cost, then i need a electrical contractor to fit earth from CU to DNO PME point and sign off
    Are you in a town or village, or somewhere more isolated?  Any neighbours with a PME system?

    If they can provide one easily, various DNOs will provide a PME terminal for a fixed rate of around £150 to £200.  If the local supply arrangements aren't suitable for PME then the DNO can refuse to provide one (on safety grounds) but might be agreeable to upgrading the local supply on a costs basis.  In that case, the ease/practicality of obtaining sufficient multiple earthing points for the PEN conductor is usually the main driver of cost.
  • gamston
    gamston Posts: 693 Forumite
    Part of the Furniture 500 Posts
    I live in the sticks, feed via a pole route single phase, but neighbour has 3 phase as when built they put in electric underfloor heating both built in mid 60's
    think it must have used water pipe as earth 
  • fenwick458
    fenwick458 Posts: 1,522 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    so the answer to the question, unfortunately nobody on here can tell you how much it will cost. I've seen the price ranging from £0, to £1500, to a flat out refusal to do it, depending on the location. only way to find out is to ring the DNO
    more often for the houses I have worked at it's been free for the homeowner, as these were just houses that had been forgotten about when the rest of the village was upgraded to PME years ago.
    actually, from what you've said "in the sticks, overhead supply" I'm going to guess upgrading it is going to be expensive. and it'd probably be cheaper getting an electrician to put some rods in
  • Risteard
    Risteard Posts: 1,951 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    gamston said:
    there is a RCD but no earth, never has been as far as i know
    yes could have earth rods but the cable run is not simple/easy, i don't want it just pegged to outside wall, want it run via loft/garage
    so i was thinking get the DNO out (thats free ?) to look and tell me if I can get PME, and cost, then i need a electrical contractor to fit earth from CU to DNO PME point and sign off

    There are also likely to be issues with the size of the main protective bonding conductors etc. It's not simply a case of make it TN-C-S now - there are particular safety requirements for a TN-C-S installation.
    RECI & Safe Electric Registered Electrical Contractor
    NICEIC Approved Contractor
    ECA Registered Member
  • Ectophile
    Ectophile Posts: 7,766 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    Many years ago, it was acceptable to use the cold water pipe as a substitute for an earth rod.  But it's not so clever as old iron/steel/lead pipes get replaced with plastic ones.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 348.2K Banking & Borrowing
  • 252.1K Reduce Debt & Boost Income
  • 452.3K Spending & Discounts
  • 240.7K Work, Benefits & Business
  • 617K Mortgages, Homes & Bills
  • 175.6K Life & Family
  • 253.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.