Hi, desperate for some advice.  I've just had a new 8.5kw shower put in.  I've also had the cable changed to 10mm from 6mm, also had a new shower pull switch fitted.  A new consumer unit was fitted in Jan 2020 with a 40amp mcb on the shower.  My problem is the new shower keeps tripping after a few mins and the mcb turns off, not the RCD, tho.  This is the second new shower I've had put in, I've had 2 electricians out and I'm still having the same problem.  Can anyone shed any light on what I can do next as I'm tearing my dirty hair out with it all as well as spending too much money.  Thanks
«1

Comments

  • will155
    will155 Posts: 2 Newbie
    First Post
    Actually just checked and it's 9.5kw, not 8.5
  • tiggerbodhi
    tiggerbodhi Posts: 415 Forumite
    Part of the Furniture 100 Posts
    IF only the MCB is tripping it is an over current issue not residual to earth, so could be a faulty cable or loose connection.
    However your on the "cusp" for a 40A MCB with a 9.5KW Shower, will be drawing 39 ish Amps operating, if the circuit test OK, sparky should have done an insulation test, it would seem normal to change the 40A MCB to a 45A MCB
    every time I manage to get one more breath into this body, I will sing a song of thanks to you my brothers, my sisters, my friends, may your sleep be peaceful, and angels sing sweetly in your ears.
  • cpbackhouse
    cpbackhouse Posts: 82 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    edited 26 May 2021 at 3:50PM
    I am not an electrician but .... at some very rough maths if its 9.5kW assuming 230V supply it could easily be pulling more than 41A which I would hope would trip the MCB rated at 40A. 
    Obviously not a professional opinion but sounds like the MCB is doing what its designed to and might need upgrading. 
    Surprised the electricians who have been out haven't mentioned this though so I might be missing something obvious.
  • Mickey666
    Mickey666 Posts: 2,834 Forumite
    1,000 Posts Photogenic First Anniversary Name Dropper
    If the MCB is tripping, and not the RCD, then it points to an over-current issue.

    UK mains voltage is specified as 230v +10% to -6% so it could be anything between 253v to 216v
    Even at the nominal 230V, 9.5kW will draw 41.3 amps so I'm not surprised that a 40A MCB trips after a few minutes as it is operating right on its limit, which is generally not advisable.

    I'm really surprised that two electricians couldn't fix the problem.  What did they say?
  • coffeehound
    coffeehound Posts: 5,741 Forumite
    Tenth Anniversary 1,000 Posts Photogenic Name Dropper
    edited 26 May 2021 at 5:10PM
    tiggerbodhi said:
     it would seem normal to change the 40A MCB to a 45A MCB
    Looking at some of the cable rating tables, it appears the shower may be drawing more than the cable is rated for in certain installation circumstances.  Perhaps that is why the electricians didn't want to uprate the MCB?
  • tiggerbodhi
    tiggerbodhi Posts: 415 Forumite
    Part of the Furniture 100 Posts
    tiggerbodhi said:
     it would seem normal to change the 40A MCB to a 45A MCB
    Looking at some of the cable rating tables, it appears the shower may be drawing more than the cable is rated for in certain installation circumstances.  Perhaps that is why the electricians didn't want to uprate the MCB?
    did, possibly wrongly, assumed that when the cable was upped to 10mm the length and type of run was taken into consideration, personally always err on the side of caution and gone for 16mm, but if it's a short run and not buried in insulation 10mm should be fine.
    every time I manage to get one more breath into this body, I will sing a song of thanks to you my brothers, my sisters, my friends, may your sleep be peaceful, and angels sing sweetly in your ears.
  • Jeepers_Creepers
    Jeepers_Creepers Posts: 4,339 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper Combo Breaker
    edited 26 May 2021 at 5:36PM
    He's had 10mm2 cable fitted, which was the right move. That should be more than capable of handling 45A - it should even be fine for a 10.8kW shower.
    Like others on here, I find the fact the 40A MCB is tripping isn't a mystery, but that two sparkies have seemingly not come to this same realisation is.
  • fenwick458
    fenwick458 Posts: 1,522 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    what brand of consumer unit have you got? 
    has anybody had a clamp meter on to see what sort of load is being drawn when the shower is on before it trips? 
    also amazed at the inability of 2 electricians to fix this, or at least do some checks so that things can be ruled out at least
  • coffeehound
    coffeehound Posts: 5,741 Forumite
    Tenth Anniversary 1,000 Posts Photogenic Name Dropper
    edited 26 May 2021 at 6:31PM
    The table shows that a ceiling installation under >100mm insulation, or in an insulated stud wall will reduce current rating to 36- or 32 amps, respectively.


  • grumbler
    grumbler Posts: 58,629 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 28 May 2021 at 8:23AM
    tiggerbodhi said:
     it would seem normal to change the 40A MCB to a 45A MCB
    Looking at some of the cable rating tables, it appears the shower may be drawing more than the cable is rated for in certain installation circumstances.  Perhaps that is why the electricians didn't want to uprate the MCB?
    ...if it's a short run and not buried in insulation 10mm should be fine.
    And what if it's a long run and not buried?
    The current will be only smaller.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.8K Work, Benefits & Business
  • 619.5K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.