PLEASE READ BEFORE POSTING: Hello Forumites! In order to help keep the Forum a useful, safe and friendly place for our users, discussions around non-MoneySaving matters are not permitted per the Forum rules. While we understand that mentioning house prices may sometimes be relevant to a user's specific MoneySaving situation, we ask that you please avoid veering into broad, general debates about the market, the economy and politics, as these can unfortunately lead to abusive or hateful behaviour. Threads that are found to have derailed into wider discussions may be removed. Users who repeatedly disregard this may have their Forum account banned. Please also avoid posting personally identifiable information, including links to your own online property listing which may reveal your address. Thank you for your understanding.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
EICR: rewiring recommended on 1930s house!
Options
Comments
-
AdrianC said:G3ralt said:
- Shower circuit is tap off in a 2.5 cable that feeds spur switch which does the shaver point C2
- fuse board no RCD protection C2
- fuse board (DB1) requires replacement not fire rated. (under the stairs) C2
- No power is present at the immersion switch further investigation required FI
- Kitchen light is on the kitchen sockets FI
- Utility light and the light under the stairs is on kitchen sockets FI
- Gas meter is not earthed C2
- Main earth is a 6mm earth C3
- Light fitting in utility has a burning smell when turned on C2
- x9 spot lights in the kitchen are not fire rated C2
- Socket in back bedroom the screws are corroded C2
- Water is not earthed C2
1. What power is the shower? 2.5mm2 cable is a bit measly for anything but a lukewarm dribbler.
2. Old fusebox, you knew that when you viewed, right?
3. The regs change all the times. They used to require metal, but then they required plastic because metal was a shock risk. Now they require metal because plastic is a fire risk.
4. Might just be a blown fuse or the immersion is switched off somewhere else.
5. Far from ideal, but not dangerous - just means that if the toaster blows the kitchen fuse, you're in the dark.
6. ...then you can't see in the cupboard either...
7. Five minute job.
8. That's one big thick beefy earth cable...
9. So change that light fitting...
10. Recessed? If you have a kitchen fire, it might spread into the ceiling a bit more easily.
11. Changing the screws takes seconds, assuming they aren't SO corroded to not come out.
12. Five minute job.Gas and water bond five minute job!! What if electrics are and back of property and gas and water at front? You could run a new cable front to back of a house and connect in five minutes?
10 wrong, having Downlights in a plasterboard ceiling you have to cut them in, therefore you’ve now taken away the fire protection from the plasterboard unless Downlights are Fire rated or fire hoods fitted on non fire rated lights.
8 wrong again, 6mm isn’t big enough currents regs state 16mm.
5 guess what wrong again! If a light has been taken off the socket circuit it hasn’t been Done by a qualified electrician, lights are wired in 1mm or 1.5mm cable. Sockets are in 2.5mm but are also wired as a ring so potentially 5mm cable to keep it simple so you understand, sockets circuits are installed onto a 32 a MCB which is far to high for a 1.5mm cable and could cause a fire.
9 would indicate to someone who actually knows about electrics that there’s more likely to a fault on the cable to the light, most likely a poorly terminated neutral. So not just a case of changing the light.I suggest if your going to try and offer people advice you actually know what your talking about as wrong advice on electrics could cause serious problems.
No Earth bond to gas and water is C2
Non fire rated lights are C3
Lights wired of sockets unless 4mm cable or 2.5mm cable with a FCU fitted before lights is a C2
Plastic fuseboard under stairs is a C3 unless there are signs of thermal damage anywhere and then it’s a C2.
I suggest that if you need a clarification on the coding for EICR then you speak to NICEIC or Napit, don’t take advice from idiots like AdrianC as he clearly doesn’t know what he’s taking about.0 -
Whilst I would not be as forthright as Chris, he is right. Unless the kitchen lights have been wired in 2.5 T+E, which is very unlikely, you’ll have lighter weight cables hanging off a 32 amp mcb. That’s a fire risk.Replacing the kitchen down lights with fireproof ones is a morning’s work, if that, and the fittings themselves are £10-20 each.Lots of 40 year old wiring is absolutely fine, but if you are going to replace it all now is the time to do it as it’s a pretty messy job.
I would not worry too much about a plastic fuse box and would look to replace the rcbs with rcbos if possible. Or maybe a new box if that’s roughly the same cost.The electrician's report and quote are very useful, and I would give them to the vendor with a request for a few £££ off the price.
No reliance should be placed on the above! Absolutely none, do you hear?0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.1K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599K Mortgages, Homes & Bills
- 177K Life & Family
- 257.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards