grumbler said:Resistance of 20m of 6mm cable is just 0.13 Ohm0
-
Her courage will change the world.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
Just an update - and yes, of course I am getting a qualified person to fit, this was just so I knew what to buy/research for my shower choices (my old house actually did have a 3 phase circuit so much for me to learn here as the cables here are quite different from there).
There were no markings on the cable apart from the manufacturer marks, AIE. So I phoned them and they confirmed that a long time ago, perhaps 20+ years, they did in fact manufacture a 6mm cable with a stranded earth core and advised that the cabling would probably be much older than 2010 when the shower was put in. So I'm going with the 8.5kw shower. The cable doesn't appear to run under the insulation, it comes out into the attic from the cavity and then back down into the shower. Our walls aren't insulated so I'm happy to run another 8.5kw shower from it. Just a shame the shower broke before I was getting an electrician in for some small jobs as I would have had that cabling redone too. Husband can't wait any longer for a shower though, its been broken since 1 day after lockdown. Thanks for all the input, I love a good electrical discussion!1 -
That's for a three-phase installation. But essentially it's due to the increased heat dissipation between the conductors and reduced losses.
1 -
The risk is primarily the heating of the cable.
Using Grumbler's figures above:
1. Heating of 6 mm cable = I x I X R = 39 x 39 x .15 = 198 watts (approx)
2. Heating of 10 mm cable = 39 x 39 x -076 = 116 watts (approx).
Those figures are the heat losses in the cable, and that for 6 mm cable approaches double that of 10 mm cable. If that heat is substantially under insulation and unable to dissipate it will raise the temperature of the insulation. In the right (wrong) circumstances could be enough to start a fire.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.3K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.4K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards