15kw cooker

Anyone care to double check my figures for me? I've just picked up a 15.9kw electric range cooker and need my figures double checking before I connect it up.

Allowing for diversity (10 amps + 30% + 5 amps due to socket) would give 22.7 amp loading. The cooker circuit is already on a 32 amp mcb with 6mm t&e and its clipped direct with a total run of less than 0.5 metre.

Sound about right?

Comments

  • bris
    bris Posts: 10,548 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Minimum I would use would be a 50amp with 10mm cable, that's a big cooker. Looking at the possibility of everything in use 32amp and 6mm is simply not enough.
  • Two
    Two Posts: 20 Forumite
    Eighth Anniversary Combo Breaker
    Is that taking diversity into account?
  • More importantly - what does the manual say?
    baldly going on...
  • Risteard
    Risteard Posts: 2,000 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    A 32A supply is considered adequate for 15kW of cooking appliances. You are fractionally over that, but the idea that you need a 50A supply is nonsense.

    You will probably find that all of those elements cannot actually be energised together, and even where they are they will cycle on and off.

    So it's possible that a 32A supply will be adequate, although a 40A may be more appropriate. Really you need an Electrician on board.

    PS your calculation is incorrect.
  • Two wrote: »
    Allowing for diversity (10 amps + 30% + 5 amps due to socket) would give 22.7 amp loading.

    You seem to have forgotten to add the 10A back in. 32.7A would be closer ...
    Proud member of the wokerati, though I don't eat tofu.Home is where my books are.Solar PV 5.2kWp system, SE facing, >1% shading, installed March 2019.Mortgage free July 2023
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.7K Banking & Borrowing
  • 253.4K Reduce Debt & Boost Income
  • 454K Spending & Discounts
  • 244.7K Work, Benefits & Business
  • 600.2K Mortgages, Homes & Bills
  • 177.3K Life & Family
  • 258.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.