Loft Conversion with Inverter in loft

Options
2»

Comments

  • Heedtheadvice
    Heedtheadvice Posts: 2,765 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 14 November 2018 at 11:46AM
    Your cupboard is of a larger size than most small switch panel cabinets so the forced (fan) ventilation is most likely not required. The presumption here is that the temperature in the closet reaches little more than the room ambient and ventilation will certainly assist that.


    The max operating environment temperature is given as 55C so if needed you can always measure that in the vicinity of the inverter. Many a roof space could reach close to that on a Sunny hot day as posted already.


    However, even if the inverter does not shut down or fail soon, bear this in mind. Most electronic equipment mean time between failures (aka it's life a without repair) shorts with increasing ambient temperature and this it is likely that you will reduce life expectancy. You will then incur more cost compared to cool running.


    As an engineering rule of thumb I aimed to have heat sinks not exceeding 35 degrees to prolong life and thus ambient temperature below that. I opted to install my inverter in a cool part of the house!


    Your decision as to if you need to move it. A trade off between the cost of that move and reduced inverter life. We do not know either but it might be worth asking the Fronius manufacturer their opinion? I could envisage over £100 to move to a cooler location.....
  • Your cupboard is of a larger size than most small switch panel cabinets so the forced (fan) ventilation is most likely not required. The presumption here is that the temperature in the closet reaches little more than the room ambient and ventilation will certainly assist that.


    The max operating environment temperature is given as 55C so if needed you can always measure that in the vicinity of the inverter. Many a roof space could reach close to that on a Sunny hot day as posted already.


    However, even if the inverter does not shut down or fail soon, bear this in mind. Most electronic equipment mean time between failures (aka it's life a without repair) shorts with increasing ambient temperature and this it is likely that you will reduce life expectancy. You will then incur more cost compared to cool running.


    As an engineering rule of thumb I aimed to have heat sinks not exceeding 35 degrees to prolong life and thus ambient temperature below that. I opted to install my inverter in a cool part of the house!


    Your decision as to if you need to move it. A trade off between the cost of that move and reduced inverter life. We do not know either but it might be worth asking the Fronius manufacturer their opinion? I could envisage over £100 to move to a cooler location.....

    I agree with all of this. In addition, we are assuming that it's a 'hot' loft space. In reality the panels themselves do add an additional layer of insulation which may make at least a little difference?
    Install 28th Nov 15, 3.3kW, (11x300LG), SolarEdge, SW. W Yorks.
    Install 2: Sept 19, 600W SSE
    Solax 6.3kWh battery
  • pinnks
    pinnks Posts: 1,548 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper Photogenic
    I agree. I reckon my loft maxed out at about 30 degrees this summer, despite the heat outside being near that too. Before I had my panels it would have been at least 10 degrees hotter. I guess the question is, do you think the temperature in the cupboard would exceed 30 degrees without some form of intervention. And, if you did nothing now and it did, could you add that ventilation in a visually acceptable way later? Could you open the back of the cupboard and super-insulate and draft proof the door?
  • Martyn1981
    Martyn1981 Posts: 15,367 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    pinnks wrote: »
    I agree. I reckon my loft maxed out at about 30 degrees this summer, despite the heat outside being near that too. Before I had my panels it would have been at least 10 degrees hotter. I guess the question is, do you think the temperature in the cupboard would exceed 30 degrees without some form of intervention. And, if you did nothing now and it did, could you add that ventilation in a visually acceptable way later? Could you open the back of the cupboard and super-insulate and draft proof the door?

    Louvre door?
    Mart. Cardiff. 8.72 kWp PV systems (2.12 SSW 4.6 ESE & 2.0 WNW). 20kWh battery storage. Two A2A units for cleaner heating. Two BEV's for cleaner driving.

    For general PV advice please see the PV FAQ thread on the Green & Ethical Board.
  • JimLad
    JimLad Posts: 950 Forumite
    Part of the Furniture 500 Posts Combo Breaker Mortgage-free Glee!
    Thank you for all your advice guys.

    For the time being I'm going to get a vent installed in the top of the cupboard (its just plasterboard above the door so will be easy) and then monitor the temperature in there when it gets to a hot point in the summer.

    The wife was talking about installing some shelves above the inverter to make use of the cupbaord space but im thinking this is probably a no no as it will stop air flow?
    Mortgage Free 22/03/17
    MissWillow is my OH!
  • JimLad wrote: »
    Thank you for all your advice guys.

    For the time being I'm going to get a vent installed in the top of the cupboard (its just plasterboard above the door so will be easy) and then monitor the temperature in there when it gets to a hot point in the summer.

    The wife was talking about installing some shelves above the inverter to make use of the cupbaord space but im thinking this is probably a no no as it will stop air flow?
    If forced air is necessary then a simple bathroom extractor fan activated by a thermostat might be an option if all else fails!
    East coast, lat 51.97. 8.26kw SSE, 23° pitch + 0.59kw WSW vertical. Nissan Leaf plus Zappi charger and 2 x ASHP's. Givenergy 8.2 & 9.5 kWh batts, 2 x 3 kW ac inverters. Indra V2H . CoCharger Host, Interest in Ripple Energy & Abundance.
  • EricMears
    EricMears Posts: 3,304 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    A roof vent might be better than a hole in top of cupboard door.
    NE Derbyshire.4kWp S Facing 17.5deg slope (dormer roof).24kWh of Pylontech batteries with Lux controller BEV : Hyundai Ioniq5
  • gefnew
    gefnew Posts: 930 Forumite
    Part of the Furniture 500 Posts Name Dropper
    hi
    if it is like the sma inverter I have it has a fan function outlet to drive a fan to remove excess heat. you will need to get a fan ,but a 5v computer fan should suffice.
    regards
    gefnew
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.8K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.8K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.8K Life & Family
  • 257.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.