  • You can use a fused connection unit either at the supply end of your 1.5mm cable, or at the terrace end, and wire your xmas lights permanently into the fused connection unit, with a 3 amp fuse. (This assumes your xmas lights are less than 100 watts total. If they are more than 100 watts you need to consider the total load already on the lighting circuit, which was reckoned at 100 watts per point or actual load if greater.)

    You must not connect a 13 amp socket to a lighting circuit without fusing down. There is always the possibility it will be used for higher loads which would overload the circuit.

    Using a 13 amp socket on a <13 amp circuit, even with fusing down as I think you suggest, is deprecated as the circuit, although partially protected, is not able to carry the full load of the socket. A long-term moderate overload will not blow a fuse, but will overload and possibly overheat the cable.

    Also, all new socket outlets must be RCD protected. If the circuit is not already RCD protected you must use an RCD socket.

    must means 'required by IET Wiring Regulations, guidance or current good practice'
    A kind word lasts a minute, a skelped erse is sair for a day.
  • FreeBear
    FreeBear Posts: 18,257 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    You must not connect a 13 amp socket to a lighting circuit without fusing down. There is always the possibility it will be used for higher loads which would overload the circuit.

    All well and good until some numpty comes along and fits a 13A fuse (or worse). As others have said, this is clearly a job for a qualified electrician, and not a job that the OP should undertake.
    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • FreeBear wrote: »
    All well and good until some numpty comes along and fits a 13A fuse (or worse).

    Yes, which is why it's deprecated, but someone changing part of the fixed wiring, including the fuse within the FCU takes responsibility for what they're doing.

    With so much stuff having plug-top power supplies it can be difficult to avoid providing a 13A socket sometimes, even though wired in would be better / safer / more compliant.
    A kind word lasts a minute, a skelped erse is sair for a day.
  • Risteard
    Risteard Posts: 2,000 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    There is no prohibition on feeding a socket outlet from a circuit with a lower rating of protective deivice. However it is mandatory that the socket outlet be RCD protected and installef by a sklled (competent) person.

    Therefore the OP must not do this job - he simply hasn't a clue what he is doing.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.