What is kVA of domestic 1phase and 3 phase supply

Getting a quote for upgrading .

Form requires this info and I’m not sure what the numbers are

Ta

Comments

  • tacpot12
    tacpot12 Posts: 9,149 Forumite
    Ninth Anniversary 1,000 Posts Name Dropper
    edited 25 July 2018 at 9:47AM
    The KVA is a measure of the power provided by the supply. For your existing single phase supply it is 230v multiplied by the size of the supply fuse, unless you know what this is, I would use 100A.

    If you are upgrading to a three phase supply, the KVA required is calculated 1.73 multiplied by 400v multiplied by the number of amps you need. If you don't know the number of amps you need yet, ask your electrician.

    I would not submit the form without having your electrician sign them off as being correct, otherwise you run the risk of a very expensive mistake.
    The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.
  • Risteard
    Risteard Posts: 1,995 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    The form isn't interested in the rating of the supply that you have. What they want to know is the capacity required (taking diversity into account).

    Someone competent will fill this in for you having been remunerated for their expert advice.
    {Signature removed by Forum Team - if you are not sure why we have removed your signature please contact the Forum Team}
  • ComicGeek
    ComicGeek Posts: 1,635 Forumite
    Eighth Anniversary 1,000 Posts Name Dropper
    Risteard wrote: »
    The form isn't interested in the rating of the supply that you have. What they want to know is the capacity required (taking diversity into account).

    Someone competent will fill this in for you having been remunerated for their expert advice.

    Indeed - I had a client who asked for 120 kVA for each of 10 houses, giving a grand total of 1200 kVA for a fairly small site. They still tried to argue it was right with UKPN, and couldn't understand why they wouldn't provide a quote for the connections...
  • Robin9
    Robin9 Posts: 12,652 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    A domestic supply may well have installed equipment - cooker, shower, water heater, lights, totalling 30 kva. But you don't use all of this at the same time and your demand may well only be 5kva.

    In the industrial market getting this right is very important because you may be on a tariff which has a capacity component - asking for 100kva and using only 30kva is an expensive mistake.
    Never pay on an estimated bill. Always read and understand your bill
  • Risteard
    Risteard Posts: 1,995 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    ComicGeek wrote: »
    Indeed - I had a client who asked for 120 kVA for each of 10 houses, giving a grand total of 1200 kVA for a fairly small site.
    LOL! Across the border the standard domestic single phase supply is 12kVA with a 16kVA "enhanced" supply available for more money. The standard supply is almost always what is taken.
    {Signature removed by Forum Team - if you are not sure why we have removed your signature please contact the Forum Team}
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.7K Work, Benefits & Business
  • 619.5K Mortgages, Homes & Bills
  • 176.3K Life & Family
  • 255.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.