What is kVA of domestic 1phase and 3 phase supply

tired_dad
Posts: 631 Forumite


Getting a quote for upgrading .
Form requires this info and I’m not sure what the numbers are
Ta
Form requires this info and I’m not sure what the numbers are
Ta
0
Comments
-
The KVA is a measure of the power provided by the supply. For your existing single phase supply it is 230v multiplied by the size of the supply fuse, unless you know what this is, I would use 100A.
If you are upgrading to a three phase supply, the KVA required is calculated 1.73 multiplied by 400v multiplied by the number of amps you need. If you don't know the number of amps you need yet, ask your electrician.
I would not submit the form without having your electrician sign them off as being correct, otherwise you run the risk of a very expensive mistake.The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.0 -
The form isn't interested in the rating of the supply that you have. What they want to know is the capacity required (taking diversity into account).
Someone competent will fill this in for you having been remunerated for their expert advice.{Signature removed by Forum Team - if you are not sure why we have removed your signature please contact the Forum Team}0 -
The form isn't interested in the rating of the supply that you have. What they want to know is the capacity required (taking diversity into account).
Someone competent will fill this in for you having been remunerated for their expert advice.
Indeed - I had a client who asked for 120 kVA for each of 10 houses, giving a grand total of 1200 kVA for a fairly small site. They still tried to argue it was right with UKPN, and couldn't understand why they wouldn't provide a quote for the connections...0 -
A domestic supply may well have installed equipment - cooker, shower, water heater, lights, totalling 30 kva. But you don't use all of this at the same time and your demand may well only be 5kva.
In the industrial market getting this right is very important because you may be on a tariff which has a capacity component - asking for 100kva and using only 30kva is an expensive mistake.Never pay on an estimated bill. Always read and understand your bill0 -
Indeed - I had a client who asked for 120 kVA for each of 10 houses, giving a grand total of 1200 kVA for a fairly small site.{Signature removed by Forum Team - if you are not sure why we have removed your signature please contact the Forum Team}0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 349.8K Banking & Borrowing
- 252.6K Reduce Debt & Boost Income
- 453K Spending & Discounts
- 242.7K Work, Benefits & Business
- 619.5K Mortgages, Homes & Bills
- 176.3K Life & Family
- 255.6K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 15.1K Coronavirus Support Boards