Electrics keep blowing
Options

colin25710
Posts: 19 Forumite


Hi
Looking for any help or advice – the toaster (previously had same problem with kettle) suddenly started to blow all the electrics, tried it in several sockets, as soon as turned on blew everything. On the MCB the main switch was off but all the others were still on, tried turning individual switches off but only when I turned everything off and turned main switch on and then all others back on did we restore power.
Bought new toaster (month ago) and today it blows power on one pair of sockets but not on another socket in kitchen – same routine required to restore power.
Any ideas what the problem could be Thanks
Looking for any help or advice – the toaster (previously had same problem with kettle) suddenly started to blow all the electrics, tried it in several sockets, as soon as turned on blew everything. On the MCB the main switch was off but all the others were still on, tried turning individual switches off but only when I turned everything off and turned main switch on and then all others back on did we restore power.
Bought new toaster (month ago) and today it blows power on one pair of sockets but not on another socket in kitchen – same routine required to restore power.
Any ideas what the problem could be Thanks
0
Comments
-
Does anything else work OK in the double socket ?Never pay on an estimated bill. Always read and understand your bill0
-
When you say main switch, the one that blows, is that the RCD switch ? Looks like this:Changing the world, one sarcastic comment at a time.0
-
are the socket on an exterior wall ? might be damp0
-
At a guess, I'd say...original toaster had developed a fault and/or one of your double sockets has a fault/is damaged.
You've replaced the toaster, but one of your sockets still has a problem.
If it were me I'd check the connections on the back of the socket but if you don't know what you're doing get an electrician in to investigate.0 -
Thanks for your replies
Stator - yes the switch that blows is the RCD
The sockets are not on an external wall
As for the sockets being faulty - we have tried other appliances (electric toothbrush, kettle ) all work fine and we had exactly the same problem with a kettle that we had to replace.0 -
It may be that the other appliances you have tested are 'double insulated' Class II products that don't use the Earth connection, and that is why you see no fault with them. A toaster would be Class I, needing an Earth.
You need the sockets testing properly.Changing the world, one sarcastic comment at a time.0 -
I can guarantee you that it won't be a Class II kettle - it will unquestionably be Class I.0
-
I have the same problem , if I used the toaster on 4 slice it would trip the electrics , so I’ve bought a new toaster it blew them again on 4 slices but if I use it on the two slice it works fine
so I’ve bought the new toaster for no reason , I’ve tried other things in the double plug and they are fine ??? Any idea’s0 -
Happened to me recently. It turned out not to be a device or a damp socket but a faulty RCD. Once that was replaced, end of problem.0
-
Toaster full of crumbs or damp?
0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.1K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599.1K Mortgages, Homes & Bills
- 177K Life & Family
- 257.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards