We're aware that some users are experiencing technical issues which the team are working to resolve. See the Community Noticeboard for more info. Thank you for your patience.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!

Wiring Double Oven and Induction Hob off one circuit?

Options
Hi there,

I have a Neff double oven that has an isolation switch. It runs off it's own dedicated radial circuit using 6mm2 cable, 5m from the consumer unit and has a 40A RCBO. The oven is rated at 4.9kW and was installed in 2014 when the flat was rewired.

I'd like to replace the current gas hob with a Neff 13A induction hob that is rated at 3kw. I make the double oven and induction hob a total 34.35A. Would it be ok to run these both off the same dedicated radial circuit and isolation switch?

This is the new hob -

http://www.neff-home.com/uk/productlist/hobs/induction-hobs/T36FB41X0G

and this is the current double oven -

http://www.neff-home.com/uk/productlist/U17S32N3GB#/Togglebox=2127537278/

Thanks
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.