Central heating questions

13»

Comments

  • System
    System Posts: 178,287 Community Admin
    10,000 Posts Photogenic Name Dropper
    edited 31 December 2017 at 11:17AM
    Phil3822 wrote: »
    This is what I want however with a hive thermostat my system will just do the on and off thing, I don't believe the boiler will modulate around the thermostat set temperature. I will await stats installation response. Thanks again.

    Your boiler will still modulate but not as much as it would with a TPI thermostat. From the Honeywell website:

    Modern controls are designed to ensure that you get the best energy efficiency
    possible from your heating system. TPI (Time Proportional & Integral) is a feature
    in your room thermostat that ensures that your boiler fires for the shortest possible
    time in order to reach and maintain your room at the comfort level selected:

    How it works:

    Firstly, there are two things you need to understand about your room thermostat:
    It has a simple memory included in its software and it ‘learns’ how the room
    temperatures are achieved and maintained. It also has a basic calculation
    capability so that it can work with the learned data and current temperatures to
    predict how long the boiler needs to be fired for.

    TPI in action:

    A TPI room thermostat works by continuously measuring the room temperature
    and calculating a difference between measured and target temperature. When the
    difference is greater than 1.5 degrees C (known as outside proportional band) it
    fires the boiler continuously
    . When the room temperature gets within 1.5 degrees C
    of the set point you have chosen on your room thermostat, the TPI software in the
    thermostat comes into action. It performs a series of calculations where it
    calculates how long the boiler needs to be fired to reach and maintain the set
    temperature. The calculation is based on the previously learnt characteristics of
    the room in which the controller is placed and the current measured temperature.
    This ‘smart’ firing of the boiler will mean that the boiler is fired just long enough to
    achieve the set temperature and no longer, thus increasing energy efficiency.


    In normal operations you will not notice any difference in how your heating system
    functions. You may, if you listen carefully, hear the boiler firing for shorter and
    shorter periods as it approaches the correct temperature. When the room set point
    is reached, you will notice that the boiler is fired for short periods in order to
    maintain the temperature. The thermostat is calculating the rate at which the room
    is losing heat and topping up with the precise amount required to counteract it.
    There is normally an overshoot of around 0.5 degrees C when first reaching set
    point. This is because the thermostat tries to reach the set point as quickly as
    possible, after that it should settle at exactly the set point. The thermostat learns
    the room’s heat loss characteristics over the first week of operation and you will
    find that the initial overshoot is higher during that period. It will quickly learn the
    characteristics and become more accurate.
    Why is this different to non TPI thermostats?
    In non TPI thermostats (commonly older devices), the boiler will continually fire
    until it gets past the set point and then when the temperature drops to a specified
    amount below the set point the boiler is then fired again. This creates greater
    temperature fluctuations and less control of your comfort levels.

    What you may notice:

    In normal operations you will not notice any difference in how your
    heating system functions. You may, if you listen carefully, hear the boiler
    firing for shorter and shorter periods as it approaches the correct
    temperature. When the room set point is reached, you will notice that
    the boiler is fired for short periods in order to maintain the temperature.
    The thermostat is calculating the rate at which the room is losing heat
    and topping up with the precise amount required to counteract it.
    There is normally an overshoot of around 0.5 degrees C when first
    reaching set point. This is because the thermostat tries to reach the set
    point as quickly as possible, after that it should settle at exactly the set
    point. The thermostat learns the room’s heat loss characteristics over
    the first week of operation and you will find that the initial overshoot is
    higher during that period. It will quickly learn the characteristics and
    become more accurate.

    Why is this different to non TPI thermostats?

    In non TPI thermostats (commonly older devices), the boiler will
    continually fire until it gets past the set point and then when the
    temperature drops to a specified amount below the set point the boiler
    is then fired again. This creates greater temperature fluctuations and
    less control of your comfort levels.

    As you can see, Honeywell's fuzzy logic will fire the boiler at maximum flow until the proportional band is reached. It is only when the system is in this band that the boiler demand will fall and the boiler will get into a condensing mode. Looking at Hive FAQs, it would appear that they have no immediate plans to build TPI into Hive.

    Finally, rather than concentrating on convenience and economy, you also need to think about failsafe options for wireless controls. For example, if my controller fails when I am away from home on a cold day, the Opentherm Bridge will default to a cycle of firing the boiler at set intervals to prevent freezing.

    Edit: As your Atag boiler is Opentherm - capable, then this link may help you decide whether the Atag One controller (or Nest) might work for you.

    https://theevohomeshop.co.uk/content/21-What-is-OpenTherm-and-why-use-Honeywell-evohome-with-it
    This is a system account and does not represent a real person. To contact the Forum Team email forumteam@moneysavingexpert.com
  • Thanks Hengus, you have been invaluable in helping me learn about the atag system and options.

    Looking through the boiler readings I am curious why the return flow temp alters. If the boiler output is at a consistent temperature why does the return temp go up over time closer to the output temp. I assume because the heat cannot be expelled from the radiators quick enough. Thanks all.
  • Raxiel
    Raxiel Posts: 1,402 Forumite
    Eighth Anniversary 1,000 Posts Name Dropper Photogenic
    Phil3822 wrote: »
    Thanks Hengus, you have been invaluable in helping me learn about the atag system and options.

    Looking through the boiler readings I am curious why the return flow temp alters. If the boiler output is at a consistent temperature why does the return temp go up over time closer to the output temp. I assume because the heat cannot be expelled from the radiators quick enough. Thanks all.

    Yes, as the house warms up, the water in the radiators will loose less heat to them.
    3.6 kW PV in the Midlands - 9x Sharp 400W black panels - 6x facing SE and 3x facing SW, Solaredge Optimisers and Inverter. 400W Derril Water (one day). Octopus Flux
  • System
    System Posts: 178,287 Community Admin
    10,000 Posts Photogenic Name Dropper
    Raxiel wrote: »
    Yes, as the house warms up, the water in the radiators will loose less heat to them.

    And as TRVs close, then the heating system effectively gets smaller. As I said earlier, all systems therefore need an open radiator without a TRV or an automatic bypass to prevent damage to the boiler.
    This is a system account and does not represent a real person. To contact the Forum Team email forumteam@moneysavingexpert.com
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.8K Work, Benefits & Business
  • 619.6K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.